Tim Mailloux
REGISTERED
My firm current has a project in design right now, and the Building official and I have a disagreement on the scope of the new sprinkler system we are adding under the projevt. The project consists of a renovation / partial change of use to an existing assembly building on a college campus, the existing building is one story type 2A construction, no sprinklers, applicable code is the 2015 IEBC, 2015 IBC and CT state amendments.
Half of the existing building (Area A) is an existing A1 Auditorium and the other half of the building (Area B) is an existing A3 gymnasium. Area B is not in in the project scope, while Area A is completely being gutted and changed into an A2 Dining hall. The renovation is a level 3 alteration and partial change of occupancy classification (IEBC 1001.3.1) under the Existing Building Code. Due to the level 3 alteration & partial change of occupancy classification We are required to install a sprinkler system in the portion of the building that is being renovated, but the BO is of the opinion that we also have to install a sprinkler system in the existing gym because of IBC 903.2.1 which states:
903.2.1 Group A. - An automatic sprinkler system shall be provided throughout buildings and portions thereof used as Group A occupancies as provided in this section. For Group A-1, A-2, A-3 and A-4 occupancies, the automatic sprinkler system shall be provided throughout the story where the fire area containing the Group A-1, A-2, A-3 or A-4 occupancy is located, and throughout all stories from the Group A occupancy to, and including, the levels of exit discharge serving the Group A occupancy. For Group A-5 occupancies, the automatic sprinkler system shall be provided in the spaces indicated in Section 903.2.1.5.
I am of the opinion that the BO if trying to push a requirement for a sprinkler system in a new A occupancy building on this project when the IEBC is clear that the sprinkler system only has to be installed in the work area undergoing the change in occupancy classification.
IEBC 904.1 Automatic Sprinkler Systems - An automatic sprinkler system shall be provided in a work area where required by Section 804.2 or this section
IEBC 804.2 Automatic sprinkler systems. Automatic sprinkler systems shall be provided in accordance with the requirements of Sections 804.2.1 through 804.2.5. Installation requirements shall be in accordance with the International Building Code.
804.2.2 Groups A, B, E, F-1, H, I, M, R-1, R-2, R-4, S-1and S-2. - In buildings with occupancies in Groups A, B, E, F-1, H, I, M, R-1, R-2, R-4, S-1 and S-2, work areas that have exits or corridors shared by more than one tenant or that have exits or corridors serving an occupant load greater than 30 shall be provided with automatic sprinkler protection where all of the following conditions occur:
1. The work area is required to be provided with automatic sprinkler protection in accordance with the International Building Code as applicable to new construction; and
2. The work area exceeds 50 percent of the floor area.
Exception: If the building does not have sufficient municipal water supply for design of a fire sprinkler system available to the floor without installation of a new fire pump, work areas shall be protected by an automatic smoke detection system throughout all occupiable spaces other than sleeping units or individual dwelling units that activates the occupant notification system in accordance with Sections 907.4, 907.5 and 907.6 of the International Building Code.
IEBC 1001.3.1 Partial change of occupancy classification - Where a portion of an existing building is changed to a new occupancy classification, Section 1012 shall apply.
IEBC 1012.1.1.2 Change of occupancy classification with separation - Where a portion of an existing building that is changed to a new occupancy classification and that portion is separated from the remainder of the building with fire barriers having a fire-resistance rating as required in the international Building Code for the separate occupancy, that portion shall comply with all of the requirements of Chapter 9 for the new occupancy classification and with the requirements of this chapter.
Commentary: When the change of occupancy classification is wholly contained in a portion of the building that is completely separated from the other uses occupying the building by fire barriers as required by Table 508.4 of the IBC, compliance with the requirements of Chapter 9 and Sections 1002 through 1012 is only required for that portion of the building occupied by the new occupancy classification. The remaining portion(s) of the building that are legally occupied are permitted to continue occupancy without change, until activities specifically covered in the code occur.
1012.2.1 Fire sprinkler system -Where a change in occupancy classification occurs that requires an automatic fire sprinkler system to be provided based on the new occupancy in accordance with Chapter 9 of the International Building Code, such system shall be provided throughout the area where the change of occupancy occurs.
Half of the existing building (Area A) is an existing A1 Auditorium and the other half of the building (Area B) is an existing A3 gymnasium. Area B is not in in the project scope, while Area A is completely being gutted and changed into an A2 Dining hall. The renovation is a level 3 alteration and partial change of occupancy classification (IEBC 1001.3.1) under the Existing Building Code. Due to the level 3 alteration & partial change of occupancy classification We are required to install a sprinkler system in the portion of the building that is being renovated, but the BO is of the opinion that we also have to install a sprinkler system in the existing gym because of IBC 903.2.1 which states:
903.2.1 Group A. - An automatic sprinkler system shall be provided throughout buildings and portions thereof used as Group A occupancies as provided in this section. For Group A-1, A-2, A-3 and A-4 occupancies, the automatic sprinkler system shall be provided throughout the story where the fire area containing the Group A-1, A-2, A-3 or A-4 occupancy is located, and throughout all stories from the Group A occupancy to, and including, the levels of exit discharge serving the Group A occupancy. For Group A-5 occupancies, the automatic sprinkler system shall be provided in the spaces indicated in Section 903.2.1.5.
I am of the opinion that the BO if trying to push a requirement for a sprinkler system in a new A occupancy building on this project when the IEBC is clear that the sprinkler system only has to be installed in the work area undergoing the change in occupancy classification.
IEBC 904.1 Automatic Sprinkler Systems - An automatic sprinkler system shall be provided in a work area where required by Section 804.2 or this section
IEBC 804.2 Automatic sprinkler systems. Automatic sprinkler systems shall be provided in accordance with the requirements of Sections 804.2.1 through 804.2.5. Installation requirements shall be in accordance with the International Building Code.
804.2.2 Groups A, B, E, F-1, H, I, M, R-1, R-2, R-4, S-1and S-2. - In buildings with occupancies in Groups A, B, E, F-1, H, I, M, R-1, R-2, R-4, S-1 and S-2, work areas that have exits or corridors shared by more than one tenant or that have exits or corridors serving an occupant load greater than 30 shall be provided with automatic sprinkler protection where all of the following conditions occur:
1. The work area is required to be provided with automatic sprinkler protection in accordance with the International Building Code as applicable to new construction; and
2. The work area exceeds 50 percent of the floor area.
Exception: If the building does not have sufficient municipal water supply for design of a fire sprinkler system available to the floor without installation of a new fire pump, work areas shall be protected by an automatic smoke detection system throughout all occupiable spaces other than sleeping units or individual dwelling units that activates the occupant notification system in accordance with Sections 907.4, 907.5 and 907.6 of the International Building Code.
IEBC 1001.3.1 Partial change of occupancy classification - Where a portion of an existing building is changed to a new occupancy classification, Section 1012 shall apply.
IEBC 1012.1.1.2 Change of occupancy classification with separation - Where a portion of an existing building that is changed to a new occupancy classification and that portion is separated from the remainder of the building with fire barriers having a fire-resistance rating as required in the international Building Code for the separate occupancy, that portion shall comply with all of the requirements of Chapter 9 for the new occupancy classification and with the requirements of this chapter.
Commentary: When the change of occupancy classification is wholly contained in a portion of the building that is completely separated from the other uses occupying the building by fire barriers as required by Table 508.4 of the IBC, compliance with the requirements of Chapter 9 and Sections 1002 through 1012 is only required for that portion of the building occupied by the new occupancy classification. The remaining portion(s) of the building that are legally occupied are permitted to continue occupancy without change, until activities specifically covered in the code occur.
- Table 508.4 does not require any separation between A2 & A3, so no fire barrier is required.
1012.2.1 Fire sprinkler system -Where a change in occupancy classification occurs that requires an automatic fire sprinkler system to be provided based on the new occupancy in accordance with Chapter 9 of the International Building Code, such system shall be provided throughout the area where the change of occupancy occurs.