Exterior exit passageways

Inspector Gadget

REGISTERED
Joined
Mar 5, 2020
Messages
1,206
Location
New Brunswick
Question for (Canadian) folks.

Exterior exit passageways, such as seen on a typical hotel: say five second-storey units, served by a covered but otherwise open-air walkway with open-air stairs at both ends.

9.9.4.2(5) exempts open-air exterior exit passageways from the fire-rated protection required for exits;
1719504346488.png

However, 9.10.8.8. says that except for some light D/E occupancies and houses, exterior exit passageways have to be fire-rated or be n/c.

1719504459793.png

I view 9.10.8.8. as prevailing, since 9.9.4.2 deals with exits only.

How do you folks deal with this?
 
Question for (Canadian) folks.

Exterior exit passageways, such as seen on a typical hotel: say five second-storey units, served by a covered but otherwise open-air walkway with open-air stairs at both ends.

9.9.4.2(5) exempts open-air exterior exit passageways from the fire-rated protection required for exits;
View attachment 13718

However, 9.10.8.8. says that except for some light D/E occupancies and houses, exterior exit passageways have to be fire-rated or be n/c.

View attachment 13719

I view 9.10.8.8. as prevailing, since 9.9.4.2 deals with exits only.

How do you folks deal with this?
They are two different concepts.
9.9.4.2(5) is about exterior passageway separated from other floor area, that is , does the exterior wall separating the exterior passageway from other floor area need to be a fire separation with fire resistance rating?
9.10.8.8 is about the fire resistance rating of the exterior passageway floor itself, that is, does the floor of the exterior passageway need a fire resistance rating?
 