2018 IBC. Given a 2 story building, VB, Sprinklered, assumed B occupancy. 2nd story has two exit stairs, one is an interior exit access stair, 2nd is a new proposed exterior exit stair.
The building is long and narrow, with each exit at the narrow end. If they were to make two spaces out of the 2nd floor, limiting access of each space to just one of the stairs are we out of t1006.3.3(2) since the story now has 2 exits? If so, then are we now only concerned with common path of egress travel (assume OL does not require two exits, and EATD is fine)? If that is the case, does the CPET get measured to the exit door leading to the stair, or all the way to the level of exit discharge? Note that per 1027.6 it does not require the exterior exit stair protection since 2 stories, so the idea that they are reaching a protected "exit" may not be the case. But if they did protect it anyway, would that make a difference?
FYI, there are 3 proposals. Two are multiple flight, switchback stairs that would exceed CPET based on a measurement from the middle point of the story, the 3rd is a straight run, which would be much closer to the 100' per t1006.2.1.
This is an existing, old building, it originally had a straight run stair, and was one single occupancy. Now they want to divide it. They tore the original straight run stair off without a permit, and with a really bad plan for the future, which went down in flames. They really want the switch backs, but they won't work because of distance to the lot line, (a straight stair will if placed in the center) but I am researching other possible issues in case they go the AMMR route with the city.
The building is long and narrow, with each exit at the narrow end. If they were to make two spaces out of the 2nd floor, limiting access of each space to just one of the stairs are we out of t1006.3.3(2) since the story now has 2 exits? If so, then are we now only concerned with common path of egress travel (assume OL does not require two exits, and EATD is fine)? If that is the case, does the CPET get measured to the exit door leading to the stair, or all the way to the level of exit discharge? Note that per 1027.6 it does not require the exterior exit stair protection since 2 stories, so the idea that they are reaching a protected "exit" may not be the case. But if they did protect it anyway, would that make a difference?
FYI, there are 3 proposals. Two are multiple flight, switchback stairs that would exceed CPET based on a measurement from the middle point of the story, the 3rd is a straight run, which would be much closer to the 100' per t1006.2.1.
This is an existing, old building, it originally had a straight run stair, and was one single occupancy. Now they want to divide it. They tore the original straight run stair off without a permit, and with a really bad plan for the future, which went down in flames. They really want the switch backs, but they won't work because of distance to the lot line, (a straight stair will if placed in the center) but I am researching other possible issues in case they go the AMMR route with the city.