cdstudio
SAWHORSE
I have a question about a project being proposed in my neighborhood and I am wondering if I am correct in my interpretation.
Brief synopsis: 25' x 100' lot with an existing small 4 story historic brownstone. The proposal is for a significant rear addition and a 5th story. It will be a 4-family (R-2) building. For the new 2nd means of egress, the Architect has an exterior "fire stair" across the back of the building (he references 1011.2) It is 6'-4" deep and 20' wide and 2'-6" from each side property line. It is a steel structure with concrete pan landings and diamond plate treads. Besides the fact that it is accessed via casement windows, how can he consider this a legal exterior fire stair and means of egress? Section 1027 has requirements for the location of exterior egress stairs, one of them being 10 ft from adjacent property lines, which would make it impossible to locate on a 25' lot. Am I missing something? To me this is just a better built fire escape. 2 internal means of egress are required (same as other projects in the neighborhood)
And just for background, I am an Architect and I volunteer for the local neighborhood assoc. to review proposed projects. I have tried talking to the applicant's Architect about it, but he is insistent that he is correct. I find it annoying since it is at the historic/planning approval stage now and has probably been in the works with the owner for at least 2 years. By the time it gets to a building code review (and assuming they agree with my interpretation and are willing to enforce it) the planning approvals/variances are already granted so amendments and redesign have to be presented to the boards again. A lot of time and money wasted for a basic code interpretation.
On a separate note, I am aware that in the planning and affordable housing community, there are proposals to remove the second means of egress requirement for small buildings (6 stories or less) Pew Research Report Link. Wondering what this forum thinks about that? Is it just creating less safe "affordable" units or creating higher rental incomes for developers?
Thanks!
Brief synopsis: 25' x 100' lot with an existing small 4 story historic brownstone. The proposal is for a significant rear addition and a 5th story. It will be a 4-family (R-2) building. For the new 2nd means of egress, the Architect has an exterior "fire stair" across the back of the building (he references 1011.2) It is 6'-4" deep and 20' wide and 2'-6" from each side property line. It is a steel structure with concrete pan landings and diamond plate treads. Besides the fact that it is accessed via casement windows, how can he consider this a legal exterior fire stair and means of egress? Section 1027 has requirements for the location of exterior egress stairs, one of them being 10 ft from adjacent property lines, which would make it impossible to locate on a 25' lot. Am I missing something? To me this is just a better built fire escape. 2 internal means of egress are required (same as other projects in the neighborhood)
And just for background, I am an Architect and I volunteer for the local neighborhood assoc. to review proposed projects. I have tried talking to the applicant's Architect about it, but he is insistent that he is correct. I find it annoying since it is at the historic/planning approval stage now and has probably been in the works with the owner for at least 2 years. By the time it gets to a building code review (and assuming they agree with my interpretation and are willing to enforce it) the planning approvals/variances are already granted so amendments and redesign have to be presented to the boards again. A lot of time and money wasted for a basic code interpretation.
On a separate note, I am aware that in the planning and affordable housing community, there are proposals to remove the second means of egress requirement for small buildings (6 stories or less) Pew Research Report Link. Wondering what this forum thinks about that? Is it just creating less safe "affordable" units or creating higher rental incomes for developers?
Thanks!