Hey! I have a general question re IBC section 705.8.
Do these wall openings regulate all portions of an exterior wall- even if they dont need to be rated?
Say for example I have an exterior wall in a building- type VB construction- with a FSD of 15' to an existing building on the same lot.
Per 705.5 The wall would not need to be rated. Do I need to still comply with opening protectives of 75% of the wall opening per 705.8?
 

705.8.1​

The maximum area of unprotected and protected openings permitted in an exterior wall in any story of a building shall not exceed the percentages specified in Table 705.8 based on the fire separation distance of each individual story.

Exceptions:

  1. 1.In other than Group H occupancies, unlimited unprotected openings are permitted in the first story above grade plane where the wall faces one of the following:
    1. 1.1.A street and has a fire separation distance of more than 15 feet (4572 mm).
    2. 1.2.An unoccupied space. The unoccupied space shall be on the same lot or dedicated for public use, shall be not less than 30 feet (9144 mm) in width and shall have access from a street by a posted fire lane in accordance with the International Fire Code.
  2. 2.Buildings whose exterior bearing walls, exterior nonbearing walls and exterior primary structural frame are not required to be fire-resistance rated shall be permitted to have unlimited unprotected openings.
 