feeding circuits through a panel

codeworks

REGISTERED
Joined
Jun 12, 2011
Messages
579
Location
South Texas
i know you cant "feed circuits through a panel "( like from one panel to another) but i cant find it in the code book. help! thanks
 
doesn't the exception allow you to run the conductors through the panel as long as you provide a barrier to isolate the conductors from the busbars? 408.3 (a)(3)
 
Are you talking about a switchboard or a panelboard?

The article cited on panelboard enclosures is generally 312.8

312.8 Enclosures for Switches or Overcurrent Devices.Enclosures for switches or overcurrent devices shall not be used as junction boxes, auxiliary gutters, or raceways for conductors feeding through or tapping off to other switches or overcurrent devices, unless adequate space for this purpose is provided. The conductors shall not fill the wiring space at any cross section to more than 40 percent of the cross-sectional area of the space, and the conductors, splices, and taps shall not fill the wiring space at any cross section to more than 75 percent of the cross-sectional area of that space.
The wiggle room is unless adequate space for this purpose is provided.

Only your inspector can say it is adequate.

I have seen guys who said that huge empty hole was not "provided" for extra conductors.
 
I agree with gfretwell.

312.8 is the proper code section and modern cabinets for panelboards are designed with adequate space for conductors to pass through or be spliced.

This section was modified in the 2011 NEC to more clearly indicated that feed trough conductors and spicing in cabinets is acceptable.

Chris
 
It would be a rare case where there isn't enough room in a panelboard to splice. Generally there is plenty of space.
 
actually, that (312.8) is what i was looking for. thanks. no splices, just fed a couple of circuits from from (through)(conduit hits bottom side of a, nipples to b, nipples to c) A, through the bottom of B to C. thought it was ok, been told it wasn't , seen it in the book, couldn't find it the other day, now i did again,thanks to you. thanks
 
This is the 2012 rewrite

312.8 Switch and Overcurrent Device Enclosures withSplices, Taps, and Feed-Through Conductors. The wiring

space of enclosures for switches or overcurrent devices

shall be permitted for conductors feeding through, spliced,

or tapping off to other enclosures, switches, or overcurrent

devices where all of the following conditions are met:

(1) The total of all conductors installed at any cross section

of the wiring space does not exceed 40 percent of the

cross-sectional area of that space.

(2) The total area of all conductors, splices, and taps installed

at any cross section of the wiring space does not

exceed 75 percent of the cross-sectional area of that

space.

(3) A warning label is applied to the enclosure that identifies

the closest disconnecting means for any feedthrough

conductors.
Notice the change in (3). You need another label.

I wonder if NFPA has a stake in the Brother P touch business? ;)
 