• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

FHA, Elevator Requirements, definition of 'Ground Floor' and 'Accessible Route'

dmoreholt

Registered User
Joined
Jan 9, 2023
Messages
13
Location
United States, Maryland
I'm doing initial research on a planned 3 story building with commercial spaces on the first floor and residences above (at least 4 units). Trying to determine if the building will require an elevator. From what I've found it appears that FHA requires ground floor units to conform with their accessibility requirements and defines ground floor units as units on the lowest floor above grade plane that are served by an accessible route. This appears to indicate that the units on the second floor of this building would be considered ground floor units. However, this building is located on very flat land and an elevator is not planned. So an accessible route was not planned. There is no easy way to get a ramp to the second floor.

Is this building exempt from FHA requirements? If not, does the requirement for an 'accessible route' require us to put in an elevator or very large ramp?
 
lowest floor above grade plane that are served by an accessible route
The lowest floor above grade plane would in this case likely be the commercial space. The residential units (unknown occupancy, but likely R-1, R-2, or R-3) would therefore be on the second story.

Now, I am no expert on FHA, but the IBC has been accepted as meeting or exceeding FHA requirements, so I'll answer based upon the IBC (2021).

I'll start by referencing IBC 1104.4. Take note that Exception #1 cannot apply given 4+ dwelling units. This section primarily relates to non-dwelling unit spaces.

1104.4 Multistory Buildings and Facilities

At least one accessible route shall connect each accessible story, mezzanine and occupied roofs in multilevel buildings and facilities.
Exceptions:
  1. An accessible route is not required to stories, mezzanines and occupied roofs that have an aggregate area of not more than 3,000 square feet (278.7 m2) and are located above and below accessible levels. This exception shall not apply to:
    1. Multiple tenant facilities of Group M occupancies containing five or more tenant spaces used for the sales or rental of goods and where at least one such tenant space is located on a floor level above or below the accessible levels.
    2. Stories or mezzanines containing offices of health care providers (Group B or I).
    3. Passenger transportation facilities and airports (Group A-3 or B).
    4. Government buildings.
    5. Structures with four or more dwelling units.
  2. Stories, mezzanines or occupied roofs that do not contain accessible elements or other spaces as determined by Section 1108 or 1109 are not required to be served by an accessible route from an accessible level.
  3. In air traffic control towers, an accessible route is not required to serve the cab and the floor immediately below the cab.
  4. Where a two-story building or facility has one story or mezzanine with an occupant load of five or fewer persons that does not contain public use space, that story or mezzanine shall not be required to be connected by an accessible route to the story above or below.
Next, go to 1108.4, which is specific to dwelling units.

1108.4 Accessible Route

Not fewer than one accessible route shall connect accessible building or facility entrances with the primary entrance of each Accessible unit, Type A unit and Type B unit within the building or facility and with those exterior and interior spaces and facilities that serve the units.
Exceptions:
  1. If due to circumstances outside the control of the owner, either the slope of the finished ground level between accessible facilities and buildings exceeds one unit vertical in 12 units horizontal (1:12), or where physical barriers or legal restrictions prevent the installation of an accessible route, a vehicular route with parking that complies with Section 1106 at each public or common use facility or building is permitted in place of the accessible route.
  2. In Group I-3 facilities, an accessible route is not required to connect stories or mezzanines where Accessible units, all common use areas serving Accessible units and all public use areas are on an accessible route.
  3. In Group R-2 facilities with Type A units complying with Section 1108.6.2.2.1, an accessible route is not required to connect stories or mezzanines where Type A units, all common use areas serving Type A units and all public use areas are on an accessible route.
  4. In other than Group R-2 dormitory housing provided by places of education, in Group R-2 facilities with Accessible units complying with Section 1108.6.2.3.1, an accessible route is not required to connect stories or mezzanines where Accessible units, all common use areas serving Accessible units and all public use areas are on an accessible route.
  5. In Group R-1, an accessible route is not required to connect stories or mezzanines within individual units, provided the accessible level meets the provisions for Accessible units and sleeping accommodations for two persons minimum and a toilet facility are provided on that level.
  6. In congregate residences in Groups R-3 and R-4, an accessible route is not required to connect stories or mezzanines where Accessible units or Type B units, all common use areas serving Accessible units and Type B units and all public use areas serving Accessible units and Type B units are on an accessible route.
  7. An accessible route between stories is not required where Type B units are exempted by Section 1108.7.
From this section take note that the only exception that can apply is #7; however, this only relates to Type B units. So, if you have any Type A units, then the story will need to be accessible.

Long answer short - yes, you will need an elevator.
 
Page 9 of the FHA Design Manual shows this requirement to provide an accessible route to the floor above the commercial space.
 

Attachments

  • IMG_0440.png
    IMG_0440.png
    541.4 KB · Views: 17
Thanks for the input. I should've noted that the applicable code here is IBC 2018. It looks like to corollary section to 1108.4 is 1107.4, and the last exemption references 1107.7, and under that section 1107.7.1.1 indicates that in buildings without an elevator service at least one story with Type B units containing an accessible entrance from the exterior is required. 1107.6.2.2.1 indicates that if we have less than 20 dwelling units (that is the case here) then no Type A units are required.

As I'm reading it, this means that if we have a single Type B unit on the ground floor with an accessible exterior entrance then an elevator would not be required and none of the other units would need to be on an accessible route or need to meet accessibility requirements. Do you all agree?
 
As I'm reading it, this means that if we have a single Type B unit on the ground floor with an accessible exterior entrance then an elevator would not be required and none of the other units would need to be on an accessible route or need to meet accessibility requirements. Do you all agree?
So you would have one residential unit on the first floor along with the commercial space?
 
It seems like the code is consistent with FHA on this question. FHA allows one unit to establish the ground floor and illustrates that on page 1.31.
 

Attachments

  • FHADM 1-31.png
    FHADM 1-31.png
    188.1 KB · Views: 18
We were hoping to find a solution that lets us do residential units on just the upper floors and not install an elevator but it appears that's not possible.
 
The lowest floor above grade plane would in this case likely be the commercial space. The residential units (unknown occupancy, but likely R-1, R-2, or R-3) would therefore be on the second story.

Now, I am no expert on FHA, but the IBC has been accepted as meeting or exceeding FHA requirements, so I'll answer based upon the IBC (2021).

I'll start by referencing IBC 1104.4. Take note that Exception #1 cannot apply given 4+ dwelling units. This section primarily relates to non-dwelling unit spaces.

1104.4 Multistory Buildings and Facilities

At least one accessible route shall connect each accessible story, mezzanine and occupied roofs in multilevel buildings and facilities.
Exceptions:
  1. An accessible route is not required to stories, mezzanines and occupied roofs that have an aggregate area of not more than 3,000 square feet (278.7 m2) and are located above and below accessible levels. This exception shall not apply to:
    1. Multiple tenant facilities of Group M occupancies containing five or more tenant spaces used for the sales or rental of goods and where at least one such tenant space is located on a floor level above or below the accessible levels.
    2. Stories or mezzanines containing offices of health care providers (Group B or I).
    3. Passenger transportation facilities and airports (Group A-3 or B).
    4. Government buildings.
    5. Structures with four or more dwelling units.
  2. Stories, mezzanines or occupied roofs that do not contain accessible elements or other spaces as determined by Section 1108 or 1109 are not required to be served by an accessible route from an accessible level.
  3. In air traffic control towers, an accessible route is not required to serve the cab and the floor immediately below the cab.
  4. Where a two-story building or facility has one story or mezzanine with an occupant load of five or fewer persons that does not contain public use space, that story or mezzanine shall not be required to be connected by an accessible route to the story above or below.
Next, go to 1108.4, which is specific to dwelling units.

1108.4 Accessible Route

Not fewer than one accessible route shall connect accessible building or facility entrances with the primary entrance of each Accessible unit, Type A unit and Type B unit within the building or facility and with those exterior and interior spaces and facilities that serve the units.
Exceptions:
  1. If due to circumstances outside the control of the owner, either the slope of the finished ground level between accessible facilities and buildings exceeds one unit vertical in 12 units horizontal (1:12), or where physical barriers or legal restrictions prevent the installation of an accessible route, a vehicular route with parking that complies with Section 1106 at each public or common use facility or building is permitted in place of the accessible route.
  2. In Group I-3 facilities, an accessible route is not required to connect stories or mezzanines where Accessible units, all common use areas serving Accessible units and all public use areas are on an accessible route.
  3. In Group R-2 facilities with Type A units complying with Section 1108.6.2.2.1, an accessible route is not required to connect stories or mezzanines where Type A units, all common use areas serving Type A units and all public use areas are on an accessible route.
  4. In other than Group R-2 dormitory housing provided by places of education, in Group R-2 facilities with Accessible units complying with Section 1108.6.2.3.1, an accessible route is not required to connect stories or mezzanines where Accessible units, all common use areas serving Accessible units and all public use areas are on an accessible route.
  5. In Group R-1, an accessible route is not required to connect stories or mezzanines within individual units, provided the accessible level meets the provisions for Accessible units and sleeping accommodations for two persons minimum and a toilet facility are provided on that level.
  6. In congregate residences in Groups R-3 and R-4, an accessible route is not required to connect stories or mezzanines where Accessible units or Type B units, all common use areas serving Accessible units and Type B units and all public use areas serving Accessible units and Type B units are on an accessible route.
  7. An accessible route between stories is not required where Type B units are exempted by Section 1108.7.
From this section take note that the only exception that can apply is #7; however, this only relates to Type B units. So, if you have any Type A units, then the story will need to be accessible.

Long answer short - yes, you will need an elevator.
No, you're reading this backwards. You need an accessible route to Type A, B, Accessible units. If you don't have them, you don't need an accessible route to them. These aren't scoping sections for unit types, its requirements for the units scoped in 1107.

See 1107.7 you probably don't need an elevator.
 