barlovian - I respectfully disagree. 508 has FOUR different methods of addressing mixed use and occupancy - you can choose any one of them. Incidental uses (508.2) is one of them. Mixed occupancies is another, which is further sub-divided into Accessory, Non-separated, and Separated. The charging statement (508.1) says "... shall comply with the applicable provisions of this section" (meaning 508). So, if you comply with 508.3.2, you have complied WITHOUT addressing incidental uses, and 508.3.2.3 says no separation required.barlovian said:The way that I read this section, separation is required. Even if you use non separated uses for height and area calculations
Section 508.2, states that incidental use shall comply with the provisions of this section or be classified as mixed use in accordance with Section 508.3Applying Section 508.3.2, Non-Separated occupancies, no separation is required between the trash room and the nursing home.
barlovian said:Kilitact--I don't see where that occurs in 508.2508.2 Incidental uses. Incidental use areas shall comply with the provisions of this section.
Exception: Incidental use areas within and serving a dwelling unit are not required to comply with this section.
[color=#FF0000 said:Plans Approver in red[/color]]508.2.1 Occupancy classification. An incidental use area shall be classified in accordance with the occupancy of that portion of the building in which it is located or the building shall be classified as a mixed occupancy and shall comply with Section 508.3. If mixed occupancy, go to 508.3, the remainder of 508.2 does not apply.508.2.2 Separation. Incidental use areas shall be separated or protected, or both, in accordance with Table 508.2.
508.2.2.1 Construction. Where Table 508.2 requires a fire-resistance-rated separation, the incidental use area shall be separated from the remainder of the building by a fire barrier constructed in accordance with Section 706 or a horizontal assembly constructed in accordance with Section 711, or both. Where Table 508.2 permits an automatic fire-extinguishing system without a fire barrier, the incidental use area shall be separated from the remainder of the building by construction capable of resisting the passage of smoke. The partitions shall extend from the floor to the underside of the fire-resistance-rated floor/ceiling assembly or fire-resistance-rated roof/ceiling ceiling assembly above or to the underside of the floor or roof sheathing, or sub deck above. Doors shall be self- or automatic closing upon detection of smoke in accordance with Section 715.4.7.3. Doors shall not have air/ transfer openings and shall not be undercut in excess of the clearance permitted in accordance with NFPA 80.
Yes. If you are going to use nonseparated mixed occupancy, then 508.2.2, 508.2.2.1, and 508.2.3 do not apply. You wrote that you were sprinklered throughout. Go directly to 508.3.2.kilitact said:My dilemma is; can I avoid the smoke dampers for the rooms addressed in my earlier post using non-separated occupancies?
The example you are reading from is for separated mixed occupancy. The B occupancy is a straight B, not mixed. The building is mixed occupancy, but, each occupancy is evaluated separately per 508.3.3.1.Examiner said:I thought that I just about had this figured out with all the responses to my post.Since the below is under Section 508.3.3 Separated Occupancies I am now confused. I thought that I read the other options 508.3.1, 508.3.2 & 508.3.3 were to be used if you did not use the Incidental Use in 508.2.
Part of the Code Commentary from Example 1 for Table 508.3.3
…The fire area containing the Group B occupancy does not require sprinklers because neither the provisions in Section 903 nor the high-rise building requirements (Section 403) apply; therefore, no sprinklers are required in any of the fire areas based on occupancy classification. Nevertheless, the requirements for incidental use areas would still be applicable within each fire area (see commentary, Section 508.2).
"Table 508.2 is applicable where an incidental use is not classified separately as to its occupancy (i.e., a mixed occupancy condition)" That's kind of a double negative, Table 508.2 is for incidental use, not mixed.Examiner said:Part of the Code Commentary from 508.2 Incidental Uses; ….Table 508.2 is applicable where an incidental use is not classified separately as to its occupancy (i.e., a mixed occupancy condition)…..
AND
….Even though incidental use areas are not considered to be mixed-use conditions, such locations may be classified separately from their occupancy and the building designed in accordance with Section 508.3 (i.e., mixed occupancies). In such cases, the presence of the higher relative fire hazard is accounted for by protection features that result from considering such areas as one of the building’s group classifications. The application of Section 508.3 will result in certain building features being governed by code requirements that are commensurate with the higher relative fire hazard of these areas.
Am I misreading something?