Hiall,
I’m working on a 4-floor church (basement + three floors) that had a main water line burst, which caused major structural damage. As part of the renovation, they’re adding an elevator and relocating the kitchen. I’m treating the basement as new space they're turning an old Sunday-school space into an entertainment and event area.
Here’s where I’m stuck. The original as-builts show a FACP and devices throughout the building, but after several walkthroughs all I’ve seen are battery-operated smoke alarms at best. There’s no sign of a functioning fire alarm system.
With the new elevator, the relocated kitchen, and the corridor connecting the two being renovated, I’m trying to figure out how to handle fire alarm coverage. The elevator will need a smoke detector, and the kitchen hood will need an Ansul system. But the church doesn’t have the budget to install a full building-wide fire alarm system. Most of the first, second and third floors are existing to remain.
Has anyone dealt with something similar? I’m wondering what the scope can end up being - can I get away with just the new areas, or does this require a full system upgrade?
Any advice or experience would be appreciated.
To my understanding the code dictates:
I’m working on a 4-floor church (basement + three floors) that had a main water line burst, which caused major structural damage. As part of the renovation, they’re adding an elevator and relocating the kitchen. I’m treating the basement as new space they're turning an old Sunday-school space into an entertainment and event area.
Here’s where I’m stuck. The original as-builts show a FACP and devices throughout the building, but after several walkthroughs all I’ve seen are battery-operated smoke alarms at best. There’s no sign of a functioning fire alarm system.
With the new elevator, the relocated kitchen, and the corridor connecting the two being renovated, I’m trying to figure out how to handle fire alarm coverage. The elevator will need a smoke detector, and the kitchen hood will need an Ansul system. But the church doesn’t have the budget to install a full building-wide fire alarm system. Most of the first, second and third floors are existing to remain.
Has anyone dealt with something similar? I’m wondering what the scope can end up being - can I get away with just the new areas, or does this require a full system upgrade?
Any advice or experience would be appreciated.
To my understanding the code dictates:
- Level 1 Alteration: Minor updates like finishes or equipment replacement. Fire alarm upgrades are usually not required unless the system is being directly modified.
- This will not apply for the basement level and kitchen area.
- Level 2 Alteration: Reconfiguration of space, changes to egress, or system upgrades. Fire alarm updates may be required in the affected areas.
- I believe this is where scope will fall into place. I will add a FACP, but devices will only be in the elevator/basement/kitchen areas.
However, a new FACP can be determined as a full upgrade?
- I believe this is where scope will fall into place. I will add a FACP, but devices will only be in the elevator/basement/kitchen areas.
- Level 3 Alteration: Work that involves more than 50% of the building area. This often triggers broader code compliance, including fire alarm upgrades
- Less than 50% is being altered.