• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

fire alarm system smokes

cda

Sawhorse 123
Joined
Oct 19, 2009
Messages
20,963
Location
Basement
in 72 is there a reference for placing smoke detectors on high ceiligngs??

or is it per manufacter listing??

looking at 29 foot ceilings

thanks
 
I saw that for heats, but there is not a similar section for smoke detectors, or refers smokes back to this section
 
High Celings?

See 5.7.3.2.3.1 TIA and then it’s the manufacturer’s listing; air flow, ceiling height; configuration; expected fire scenario and Annex B4. Since the ceiling heights are reaching various listing heights the use of engineering analysis for fire flows and stratification potentials is necessary and potential closer spacing than the standard 30 foot rule for smooth ceilings may need consideration by the designer.
 