In most of the Assembly areas, in IBC section 903.2.1, one of the triggers for providing a sprinkler system is "The fire area exceeds 12,000 sqft".
I have a 2-story, main occupancy is A-3, building addition that is set into a hill. Each floor has around 9000 sqft, and each floor has grade access. The building has an total occupant load of under 3000 sqft. This is attached to another A-3 building, but these 2 buildings are separated by a 2-hour firewall, based on IBC table 706.4. The existing building is not sprinklered, due to code rules when that was built.
I have an elevator to connect the two levels. I also have an open stair to connect each level, so I cannot provide a 2-hr floor separation.
Is this 12,000 sqft fire area, the aggregate of both floor 1 and floor 2, which would give me a total of 18,000 sqft, thus requiring a sprinkler system, or is this fire area only based on 1 level, which puts me under this requirement, thus no sprinkler system?
Thanks.
I have a 2-story, main occupancy is A-3, building addition that is set into a hill. Each floor has around 9000 sqft, and each floor has grade access. The building has an total occupant load of under 3000 sqft. This is attached to another A-3 building, but these 2 buildings are separated by a 2-hour firewall, based on IBC table 706.4. The existing building is not sprinklered, due to code rules when that was built.
I have an elevator to connect the two levels. I also have an open stair to connect each level, so I cannot provide a 2-hr floor separation.
Is this 12,000 sqft fire area, the aggregate of both floor 1 and floor 2, which would give me a total of 18,000 sqft, thus requiring a sprinkler system, or is this fire area only based on 1 level, which puts me under this requirement, thus no sprinkler system?