• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Fire area

Gordon65

Registered User
Joined
Jan 17, 2021
Messages
12
Location
Geneseo, IL
When considering fire area, are bathrooms, stairs included in the fire area? Would be using NET occupancy. Where in the code would I find this information?

Thanks
 
Definitions:

[BE] FLOOR AREA, NET. The actual occupied area not
including unoccupied accessory areas such as corridors,
stairways, ramps, toilet rooms, mechanical rooms and closets.
 
Disregard, I see you are asking Fire Area, those areas you describe above would be included.

Definitions

[BF] FIRE AREA. The aggregate floor area enclosed and
bounded by fire walls, fire barriers, exterior walls or horizontal
assemblies of a building. Areas of the building not provided
with surrounding walls shall be included in the fire area
if such areas are included within the horizontal projection of
the roof or floor next above.
 
When considering fire area, are bathrooms, stairs included in the fire area? Would be using NET occupancy. Where in the code would I find this information?

Thanks


The aggregate floor area enclosed and
bounded by fire walls, fire barriers, exterior walls or horizontal
assemblies of a building.

For your question, it will be the entire barn,

If the addition has one of the above, it should have a separate fire area.
 
Disregard, I see you are asking Fire Area, those areas you describe above would be included.

Definitions

[BF] FIRE AREA. The aggregate floor area enclosed and
bounded by fire walls, fire barriers, exterior walls or horizontal
assemblies of a building. Areas of the building not provided
with surrounding walls shall be included in the fire area
if such areas are included within the horizontal projection of
the roof or floor next above.
Thank you
 