I wanted to double check my knowledge on fire areas:
FIRE AREA. The aggregate floor area enclosed and bounded by fire walls, fire barriers, exterior walls or horizontal assemblies of a building. Areas of the building not provided with surrounding walls shall be included in the fire area if such areas are included within the horizontal projection of the roof or floor next above.
This does not include occupancy separations in TABLE 508.4 REQUIRED SEPARATION OF OCCUPANCIES (HOURS) correct?
Assuming that is correct, what is the correct term for the separated areas created by TABLE 508.4 REQUIRED SEPARATION OF OCCUPANCIES (HOURS) if you don't call them fire areas? I guess you call them separated group A, separated group B, etc if there were multiple occupancy types in each group?
Thanks!
FIRE AREA. The aggregate floor area enclosed and bounded by fire walls, fire barriers, exterior walls or horizontal assemblies of a building. Areas of the building not provided with surrounding walls shall be included in the fire area if such areas are included within the horizontal projection of the roof or floor next above.
This does not include occupancy separations in TABLE 508.4 REQUIRED SEPARATION OF OCCUPANCIES (HOURS) correct?
Assuming that is correct, what is the correct term for the separated areas created by TABLE 508.4 REQUIRED SEPARATION OF OCCUPANCIES (HOURS) if you don't call them fire areas? I guess you call them separated group A, separated group B, etc if there were multiple occupancy types in each group?