New build 20,000' divided into 3500' units. This is a metal building.
Fully sprinklered
Question I have is it appears I need a one hour rated wall.
I intended to use 3 5/8" metal studs with 5/8" Type X drywall.
Since one layer of 5/8" is rated for one hour do I need it on both sides or can I use say 1/2" standard on the opposite side.
Most examples show 5/8's type X on both sides.
Some examples also show insulation inside the wall, I don't think it's required
Last point.
CHAPTER 25 GYPSUM BOARD AND PLASTER SECTION 2501
2508.4 Joint treatment.
Gypsum board fire-resistance-rated assemblies shall have joints and fasteners treated.
Exception: Joint and fastener treatment need not be provided where any of the following conditions occur:
3. Square edge or tongue-and-groove edge gypsum board (V-edge), gypsum backing board or gypsum sheathing.
If I'm reading this correctly the drywall can be unfinished?
Fully sprinklered
Question I have is it appears I need a one hour rated wall.
I intended to use 3 5/8" metal studs with 5/8" Type X drywall.
Since one layer of 5/8" is rated for one hour do I need it on both sides or can I use say 1/2" standard on the opposite side.
Most examples show 5/8's type X on both sides.
Some examples also show insulation inside the wall, I don't think it's required
Last point.
CHAPTER 25 GYPSUM BOARD AND PLASTER SECTION 2501
2508.4 Joint treatment.
Gypsum board fire-resistance-rated assemblies shall have joints and fasteners treated.
Exception: Joint and fastener treatment need not be provided where any of the following conditions occur:
3. Square edge or tongue-and-groove edge gypsum board (V-edge), gypsum backing board or gypsum sheathing.
If I'm reading this correctly the drywall can be unfinished?