Hi everyone. Working with a R-2 building. There is a corridor connecting the dwelling units (1 hour fire partition at the corridor).
For doors from dwelling units into the corridor, I had thought per Table 716.1(2) that the doors would be required to be rated 20 minutes under the fire partition "corridor" row. However... my commentary confused me by stating that "1/3 hour doors are required for corridors and 3/4 hour doors are required for dwelling and sleeping unit separations."
I guess the wall between the corridor and the dwelling unit is both a corridor wall and a wall serving as a dwelling unit separation. I don't know what scenario there would be a door between residential dwelling units so I'm not sure what the commentary is saying exactly, if it's NOT referring to my scenario.
Just checking... you all interpret this condition as requiring 20 minutes, right?
For doors from dwelling units into the corridor, I had thought per Table 716.1(2) that the doors would be required to be rated 20 minutes under the fire partition "corridor" row. However... my commentary confused me by stating that "1/3 hour doors are required for corridors and 3/4 hour doors are required for dwelling and sleeping unit separations."
I guess the wall between the corridor and the dwelling unit is both a corridor wall and a wall serving as a dwelling unit separation. I don't know what scenario there would be a door between residential dwelling units so I'm not sure what the commentary is saying exactly, if it's NOT referring to my scenario.