• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

fire hose cabinets vs fully sprinklered buildingl

John shane

Registered User
Joined
Feb 13, 2020
Messages
12
Location
California
Any latest code reference I can refer to where it says that fully sprinklered buildings does not need fire hose cabinets. Were going on a debate with the owner.
 
There are only two instances in the IBC that require the installation of a hose:
  1. Stages > 1000 sq. ft.; Class III standpipe and hose; or Class II standpipe and hose with sprinkler system (Section 905.3.4, 2018 IBC)
  2. Stages, the rear of an auditorium on each side, each side of a balcony, and each tier of dressing rooms in Groups A-1 and A-2 with occupancies exceeding 1000 persons; Class II with 100-foot hose whether sprinklered or not (Section 905.5, 2018 IBC)
 
And if the building has a sprinkler system required by an applicable building code the installation and design standard referenced by that building code allows the AHJ to have occupant intended hose to be removed in accordance with NFPA 13, 2016 or 2019 [8.17.5.1.2.2].

The maintenance testing and flushing would be in accordance with [27.1] and NFPA 25, 2017 [6.4.1 to Table 6.1.1.2] as referenced.
 