• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Fire Hydrant Minimum and Maximum Height

Saber Elkassas

Registered User
Joined
May 25, 2021
Messages
12
Location
Egypt
Hello,

I have a clarification regarding the minimum and maximum height of the hydrant outlet as referred in NFPA 24 2019:

"7.3.3* The center of a hose outlet shall be not less than 18 in. (450 mm) above final grade.
7.3.3.1 The center of a hose outlet shall not be more than 36 in. (900 mm) above final grade."

Which hose outlet is the concerned here in these sections, the 2.5" outlets or the 5" pumper connect?
 
Te center line of most modern hydrant ports is all on the same plane


But if you do it to the middle of the 2.5, is it possible the five inch would either be a little in the ground, or so close that you could not spin on the hose?
 
But if you do it to the middle of the 2.5, is it possible the five inch would either be a little in the ground, or so close that you could not spin on the hose?
What TheCommish stated that I agree with is that on most hydrants available today the centerline of all of the outlets is the same as it doesn't matter which port you measured to since the code specifies the centerline of the outlet.
 
Other ways to look at it is if you cannot spin a standard hydrant wrench which is around 18 inches long it is to close to the ground and the bolted flange is designed to be about 2 inches above grade, so the contractor has to order the correct buried barrel length for the main
 
What TheCommish stated that I agree with is that on most hydrants available today the centerline of all of the outlets is the same as it doesn't matter which port you measured to since the code specifies the centerline of the outlet.


There are those funny looking California WET hydrants, with all different level outlets!!!
 
True, for a wet barrel I would go with the CL of lowest port. Then there is Boston which in about 200 a cording to my shoce took all the Lowrey Chuck flush mount hydrants off their engines1624320428483.png


and airport with hydrant in the ground.