• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Fire partition continuity IBC 2018

khsmith55

Bronze Member
Joined
Oct 23, 2010
Messages
237
Location
Glenwood Springs, CO
Looking at the termination of corridor walls and non-rated partitions at a 1 hour floor/ceiling above.

IBC 2015 Section 714.4.2, Exception 7, states:
The ceiling membrane of 1- and 2-hour fire resistance-rated horizontal assemblies is permitted to be interrupted with the double wood top plate of a wall assembly that is sheathed with Type X gypsum wallboard, provided that all penetrating items through the double top plates are protected in accordance with Section 714.4.1.1 or 714.4.1.2 and the ceiling membrane is tight to the top plates.

It appears this exception "went away" or may have been relocated in the 2018 IBC. Can someone give me some direction?
Thanks in advance.