Fire protection required for canopies?

chris macko

REGISTERED
Joined
Dec 3, 2021
Messages
25
Location
Chicago
I've got a campus project with a number of buildings, many with hazardous occupancies. One "building" is just an open storage yard with containment curbs, and a small canopy over a truck unloading area. If this was a building, it would fall under H-3/H-4 and require sprinklers no matter how small, but since it has no walls, my thought it it's not a building. The fire protection contractor is arguing that we need to provide sprinklers under it and add a fire riser since it's a projection over 4ft in width under NFPA 13, which I thought was only for canopies attached to a larger building. Is there anything in the code that would require sprinkling an exterior, unenclosed canopy, particularly when combustible materials are being handled beneath it?
 
I'd have to see it, but freestanding canopies not associated directly with a building and not really sheltering an occupancy are a U IMHO....Otherwise every gas station would be an H....
 
Every gas station I've seen with a canopy has an automatic extinguishing system. It's not a sprinkler system, but it is an extinguishing system.
 