• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Fire Pump Room Electrical Requirements NEC 695

Exception to 695.6(A)(2)(4):
The supply conductors located in the electrical equipment room where they originate and in the fire pump room shall not be required to have the minimum 2-hour fire separation or fire-resistance rating unless otherwise required by 700.10(D) of this Code.
 
Exception to 695.6(A)(2)(4):
The supply conductors located in the electrical equipment room where they originate and in the fire pump room shall not be required to have the minimum 2-hour fire separation or fire-resistance rating unless otherwise required by 700.10(D) of this Code.
In this case, the conductors in question start 2 rooms over and go through the trash room.
 