Fire Pump Test Header - Is it required?

FyrBldgGuy

Silver Member
Joined
Oct 19, 2009
Messages
356
Does a fire pump require a test header rather than just a water flow metering device?

If you believe that it does not require a test header please state your reasons why it is not required.
 
A "test header" is not specifically required, but a specific amount of hose valves is needed somewhere in the system, capable of discharging the full capacity of the fire pump (see Table 5.25(a)). Even without a fire pump, the forward flow backflow preventer test, required annually, needs a place to dump several hundred or thousand GPM.

Stringing hose from several standpipes would meet code, but why not just do it right? As an AHJ, ask the plan submitter how the annual testing will be accomplished.
 
Dr. J I agree 100%. You can not do an acceptance test via a flow meter. The valves to the city water supply can be shut 100% and you will never know it with a flow meter that is piped back to the suction side of a pump. Now if the meter is to a tank or drain that can handle 150% flow rating that is a different story.
 
Last edited by a moderator:
I agree with Dr. J and Insurance Engineer. At acceptance testing and every third year a test is required and a closed loop is not acceptable.

The exception to a test header is where it is "not possible". Somehow that has become a norm rather than an exception.
 
CDA - you are not wrong.

A test header is NOT required, but a means of testing is. Another reason to not use a test header (Besides being "not possible" or being cheap) is to prevent people from messing with exterior mounted test header valves. Just need to make sure there is SOME way of testing both a fire pump and the backflow preventer.
 