• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Fire rated ceiling

Inspector 102

Silver Member
Joined
Oct 22, 2009
Messages
356
Location
N/E Indiana
In review of a fire rated assembly, GA File No. FC 5750, I do not see any requirement for the individual layers of gypsum board to be mud/taped between layers. Is there a specific location that this requirement is found or is it not required because of the staggered joint application? Thank you.
 
In GA-600, look at the "General Explanatory Notes." Note 6 addresses the finishing of gypsum board and only requires the face layers (i.e., exposed layers) to have joints taped and finish to Level 1 per GA-214 and fastener heads treated. It further states that base layers in multi-layer systems do not require joints or fasteners taped or treated.
 