Many of the manufactures have rated to nonrated assemblies.garrett said:It is unfortunate that the GA manual lacks assembly details for intersections.For example, where a rated wall is intersected by a non-rated wall or by a non-rated floor assembly.
It seems a lot of designers just invent details that might seem plausible,
But have not actually been tested and listed.
Or am I missing something?
UL lacks details for intersections as well...what's your point?garrett said:It is unfortunate that the GA manual lacks assembly details for intersections. For example, where a rated wall is intersected by a non-rated wall or by a non-rated floor assembly. It seems a lot of designers just invent details that might seem plausible, But have not actually been tested and listed. Or am I missing something?
You can't and therfore that dseign would not be permittedhow does one maintain the fire-resistive rating of a multi-story rated wall when there is a non-rated floor/ceiling assembly that intersects it and bears on it at intermediate levels. This occurs at townhouses sharing a common wall.
Once again, refer to manufactures Area Separation Fire Wall Details. If you test an assembly as you describe, it will fail.garrett said:Well, for example, how does one maintain the fire-resistive rating of a multi-story rated wall when there is a non-rated floor/ceiling assembly that intersects it and bears on it at intermediate levels. This occurs at townhouses sharing a common wall.
Seems simple enough, but researching precedents I find that the majority of the time architects details are not based on an actual tested assembly, but something that is invented to look reasonable enough.
It would be nice if UL had some drawings of conditions like these that are tested.
What do you mean, "you can't?"mtlogcabin said:You can't and therfore that dseign would not be permitted.
The situation I describe is NOT an Area Separation Fire Wall, it is a 1-hour fire-resistive common wall, per R302.2, Excpetion.mark handler said:Once again, refer to manufactures Area Separation Fire Wall Details. If you test an assembly as you describe, it will fail.
My recommendation would be to hire an architect familiar with the typology.garrett said:Well, for example, how does one maintain the fire-resistive rating of a multi-story rated wall when there is a non-rated floor/ceiling assembly that intersects it and bears on it at intermediate levels. This occurs at townhouses sharing a common wall.
:agreebrudgers said:My recommendation would be to hire an architect familiar with the typology.
You were given constructive advice which you chose to ignor.garrett said:I appreciate more constructive advice.
I think he is practicing as or like an architect...and the advice would have been better directed to the Owner.mark handler said:You were given constructive advice which you chose to ignor.