Fire rating for structural members in IIB construction

tuzi

REGISTERED
Joined
Jun 14, 2016
Messages
50
Location
Colorado
I am referencing the 2021 IBC as adopted in Maryland. In Type IIB construction, primary structural members such as columns and beams are not required to be fire-resistance rated per Table 601, unless another code provision—such as proximity to property lines, occupancy separations, or specific use conditions—requires otherwise.
Did I interpret correctly?

Thanks,
 
unless another code provision—such as proximity to property lines, occupancy separations, or specific use conditions—requires otherwise.
Did I interpret correctly?
Yes, you interpreted Table 601 Fire-Resistance Rating Requirements for Building Element correctly.

such as proximity to property lines, occupancy separations, or specific use conditions—requires otherwise.
Yes, any other code provisions would apply. But in the case of rating structural elements…

1. Proximity to property lines affects the rating and amount of openings in exterior walls, it doesn’t affect the rating of elements inside the building envelope.
2. Per IBC 508.4.4.1, occupancy separations per Table 508.4 are the ratings required for the fire barrier or horizontal assembly used for the separation - you don’t have to rate the structural frame, but if something happens to fall within a fire barrier it will also happen to be protected by the fire barrier.
3. Regarding special use conditions, I can’t think of anything off the top of my head that requires rating of structural elements in Chapter 4, wouldn’t hurt to check to see if something applies.

as adopted in Maryland
Sorry, I can’t speak to any specific changes Maryland may have made.
 
unless another code provision
any other code provisions would apply
Should have though to mention this when I mentioned fire barriers, but a good example of a code provision that would require rating part of the structural frame would be the requirement for rating supporting construction for fire barriers per IBC 707.5.1.

Here’s a recent post that talks about supporting construction:
 