[F] 903.2 Where required.
Approved automatic sprinkler systems in new buildings and structures shall be provided in the locations described in Sections 903.2.1 through 903.2.12.
Exception: Spaces or areas in telecommunications buildings used exclusively for telecommunications equipment, associated electrical power distribution equipment, batteries and standby engines, provided those spaces or areas are equipped throughout with an automatic smoke detection system in accordance with Section 907.2 and are separated from the remainder of the building by not less than 1-hour fire barriers constructed in accordance with Section 707 or not less than 2-hour horizontal assemblies constructed in accordance with Section 711, or both.
THE NFPA standard itself has the ability to remove fire sprinkler systems from electrical rooms as long as the conditions of NFPA 13 2016 section 8-15.11.2 are met (these requirements are similar as NFPA 13 -1996 edition section 4-13.10)
FYI, having a major fault and heavy arcing involved with heavy duty electrical (high voltage) equipment may not be the best thing to interject water into it.....
The exception listed in NFPA has several conditions: (all have to be met)
room dedicated to electrical equipment only
Only dry type electrical equipment used
Equipment is installed in a 2 hour fire rated enclosure
No combustible storage allowed.