George McGerd
Bronze Member
Per my interpretation of IBC 2012 - 1022.7 and with respect to protecting exterior walls OR stairway enclosure walls that form an angle less than 180º, my understanding of the requirement is that you must protect either the stair enclosure wall OR the building wall for a minimum distance of 10 feet with a rating of 1-hr to meet this requirement. I have a unique situation where there is exit door from the stairway AND a window in this corner of the building and BOTH are within 10 feet of the 90º angle (see attachment). I'd like to fire-rate the stair enclosure (and exit door) ONLY so that I don't have to rate the building exterior wall AND the window. However, the AHJ is saying I must also rate the window due to the fact that it is so close to the point of exit discharge. Is there anything in the code that requires openings near points of exit discharge to be rated or is my AHJ just exercising his due authority to require this window to be rated?Thanx.
View attachment 2092
scan1.pdf