A 1 or 2 hour rated wall on a slab on grade, is the base of the wall supposed to be fire caulked if the drywall is tight to the floor? IBC 2022. there are bottom of wall fire resistive joint systems that show a gap in drywall that is filled with caulk but ive never specified it this way, only at top of walls or other locations that have a legitimate gap in construction. I have seen UL wall assemblies that show an optional sealant at the base but no fire caulk specified. I have a builder client who we did not do the plans for saying that the AHJ is saying the base of wall needs to be fire caulked. The client is looking for me to provide a code section that says they don't need to fire caulk the base of the wall...have i been getting away with one on not having this detail specified?
Assembly
Diagram
Joints installed in or between fire-resistance-rated walls, floor or floor/ceiling assemblies and roofs or roof/ceiling assemblies shall be protected by an approved fire-resistant joint system designed to resist the passage of fire for a time period not less than the required fire-resistance rating of the wall, floor or roof in or between which the system is installed.
Exception: Fire-resistant joint systems shall not be required for joints in the following locations:
715.3 Fire-Resistance-Rated Assembly Intersections
AssemblyDiagram
Joints installed in or between fire-resistance-rated walls, floor or floor/ceiling assemblies and roofs or roof/ceiling assemblies shall be protected by an approved fire-resistant joint system designed to resist the passage of fire for a time period not less than the required fire-resistance rating of the wall, floor or roof in or between which the system is installed.
Exception: Fire-resistant joint systems shall not be required for joints in the following locations:
- Floors within a single dwelling unit.
- Floors where the joint is protected by a shaft enclosure in accordance with Section 713.
- Floors within atriums where the space adjacent to the atrium is included in the volume of the atrium for smoke control purposes.
- Floors within malls.
- Floors and ramps within parking garages or structures constructed in accordance with Sections 406.5 and 406.6.
- Mezzanine floors.
- Walls that are permitted to have unprotected openings.
- Roofs where openings are permitted.
- Control joints not exceeding a maximum width of 0.625 inch (15.9 mm) and tested in accordance with ASTM E119 or UL 263.
- The intersection of exterior curtain wall assemblies and the roof slab or roof deck.