Fire separation for storage?

EricWatkins

Member
Joined
Apr 27, 2015
Messages
31
Location
Decatur Il
Hello everyone,

Forgive me because I am a mere mechanical inspector but trying to figure out something that is more directly IBC related.

We used to have a plans examiner in our department but when the city down-sized 1 and a half years ago, they eliminated his position, and the guy was brilliant. It was a true loss of knowledge in our department.

To the point, we have a retail store (a Dollar General) which is basically finished and the general contractor is calling for final inspections. The store is just a retail sales space, not sprinkled, and has an 1,100 sq ft storage space in the back. The plans did not call for a fire separation, but I had it in my head that this type of situation had to be fire separarted between the storage space and the retail space if it wasn't sprinkled and over 100 sq ft. Did I just somehow come across wrong info at some point and it stuck in my head, or is this somewhere in the IBC or IFC which I couldn't locate after about 45 minutes of searching?

Any help would be much appreciated. Thank you!

Eric
 
in most occupancies, Seperation is no longer required unless it exceeds 10% of the area of the main use.
 
EricWatkins said:
Hello everyone,Forgive me because I am a mere mechanical inspector but trying to figure out something that is more directly IBC related.

We used to have a plans examiner in our department but when the city down-sized 1 and a half years ago, they eliminated his position, and the guy was brilliant. It was a true loss of knowledge in our department.

To the point, we have a retail store (a Dollar General) which is basically finished and the general contractor is calling for final inspections. The store is just a retail sales space, not sprinkled, and has an 1,100 sq ft storage space in the back. The plans did not call for a fire separation, but I had it in my head that this type of situation had to be fire separarted between the storage space and the retail space if it wasn't sprinkled and over 100 sq ft. Did I just somehow come across wrong info at some point and it stuck in my head, or is this somewhere in the IBC or IFC which I couldn't locate after about 45 minutes of searching?

Any help would be much appreciated. Thank you!

Eric
Plans examiners are overrated

Anyway. Which edition of ibc are you under??
 
but I had it in my head that this type of situation had to be fire separarted between the storage space and the retail space if it wasn't sprinkled and over 100 sq ft. Did I just somehow come across wrong info at some point and it stuck in my head, or is this somewhere in the IBC or IFC which I couldn't locate after about 45 minutes of searching?
The 2006 IBC did require storage rooms over 100 sf to be separated or protected. Your memory is current, but current codes have changed.
 
As long as the Fire Area does not exceed 12,000 sq ft then it is a mixed non-separated use and does not require sprinklers even if the storage area exceeds 10%
 
Not sure if IL or your jurisdiction is an NFPA 101 area, but for what it's worth, NFPA 101 requires the storage area to be 1-hour separated or sprinklered in a Mercantile Occupancy that is not fully sprinklered.
 