iggentleman
Bronze Member
I was at a 2009 IBC training workshop earlier this week. We were talking about fire separation strategies for elevator lobbies in high rise buildings and the presenter made a statement that the fire service elevator and the accessible occupant evacuation elevator needed to be in their own separate shafts. Some of us questioned that statement and there was a short discussion. Even though he couldn’t come up with the code citation, the presenter still thought that the special elevators could not share shafts with other elevators.
I’ve looked through the 2009 IBC and could not find this requirement. 3002.2 says a maximum or 4 elevators in a shaft. 3007.2 and 3008.9 only requires the hoistway enclosure to meet section 708. Section 708 addresses the enclosure, fire rating and elevator lobbies but says nothing about requiring a separate shaft.
Am I missing a provision buried somewhere in the IBC? Is there something in ASME 17.1 or another elevator code that would require enclosures separate from other shafts. Has anyone come across this before?
I’ve looked through the 2009 IBC and could not find this requirement. 3002.2 says a maximum or 4 elevators in a shaft. 3007.2 and 3008.9 only requires the hoistway enclosure to meet section 708. Section 708 addresses the enclosure, fire rating and elevator lobbies but says nothing about requiring a separate shaft.
Am I missing a provision buried somewhere in the IBC? Is there something in ASME 17.1 or another elevator code that would require enclosures separate from other shafts. Has anyone come across this before?