nfpa 80 1999
6-3 Openings.
6-3.1 Frames.
Frames shall not be required for rolling steel door installations. Where frames or jambs are provided, only minimum 3/16-in. (4.76-mm) nominal structural steel or formed steel plate shall be used. Frames or jambs shall be in accordance with the door manufacturer’s listing.
6-4 Assembly Components.
6-4.1 Closing Devices.
6-4.1.1
An automatic-closing device shall be installed on every rolling steel door.
6-4.1.2
Rolling steel doors shall close automatically upon activation or release of a fusible link or detector.
6-4.1.3
The automatic-closing mechanism shall be enclosed in a metal housing to protect the mechanism from debris and ensure operation in the event of fire.
6-4.1.4
A governor, where employed on a door, shall be an integral mechanism working in coordination with the closing device and shall control the closing speed of the door.
6-4.1.5
Rolling steel fire doors shall have an average closing speed of not less than 6 in./sec (152 mm/sec) nor more than 24 in./sec (610 mm/sec).
MINIMUM 6 inches a second, so a ten foot high door would take 20 seconds??? to MAX 24 inches 5 seconds
so does the door meet NFPA 80??