Fire Sprinkler Coverage Question
Marshal Chris
Silver Member
Long Island, NY
Looking for some insight here.
Type V construction R-1.
Second floor deck has sprinkler protection under it, combustible stairs do not. I believe they are required. I'm going to start digging into 13.
Thanks!
Re: Fire Sprinkler Coverage Question
are you doing 13 or 13 R??
interior or exterior??
could possibly use the four foot rule???
are there heads above the stairs??
Sorry, I need to clarify further.
All rooms access is from a combustible deck. There is sprinkler under the decking, since it's type V. the only exits from the second floor are by means of a tyle V stair which has no protection under it.
It makes me scratch my head that we protect the decking but not the stairs. Hence my qustion.
CDA, can you elaborate on the four foot rule?
Answer NFPA 13 R ---6.6.5* Sprinklers shall not be required in any porches, balconies,
corridors, carports, and stairs that are open and attached.
However, The Building Code and Fire Code State
[F] 903.3.1.2.1 Balconies and decks. Sprinkler protection
shall be provided for exterior balconies, decks and
ground floor patios of dwelling units where the building
is of Type V construction.
Therefore, the poject as described (if a 13 R system - appears to be code complaint since the standards doesn't requrie it and the code provisions ( which supercede the standard requirements) do not require open stairs that are attached to be protected.
just MHO, yours may differ, especially if you are the AHJ....
with out seeing sprinkler and building plans, would say that if you are sprinling under an exterior combustible walk way, and the stairs are attached to said walk way, I would require the underside of the stairs to be protected if not open grate and over four feet.
I guess a question is on 2nd floor is there a overhang over said """ All rooms access is from a combustible deck."""" and if so is this sprinkled??????
just trying to fiqure out why the first floor is protected??? since it is exterior access to the rooms
First floor is protection outside the rooms is really protecting the combustible deck for the second floor. Second floor has about a 6 inch overhang from the roof and the rest if open air.
Sprinklers are required outside according to the building code as BB noted above. for stairs, sprinklers are required top and bottom only.
NFPA 13-8.15.3.1 Combustible Construction. Sprinklers shall be installed beneath all stairways of combustible construction.
That makes it sound like it's required to me. Comments?
you can try , it does fall under shaft section???
I think I would use the four foot rule and also because it is part of the exit way, and possible storage underneath
are you in the plan review stage or is this installed already and the inspection stage???
This job was a tragedy from the start. The business owner started putting in the system himself without permits. This has been 5 years in the making. They now have a contractor and I found a bunch of deficiencies at the hydrostatic test.
:cry: :cry: :cry:
sprinklers in stairways .. make a scary miserable situation even more miserable.
Last type V hotel I stayed in.. no sprinklers in the stairway (but an added bonus of irregular risers.. tripped alot getting to the 3rd floor)...
My biggest issue with sprinklering the decks.. it's got to be a dry system in most areas.. I'm not a fire designer, but as I read 13R.. it should be a separate branch line for the dry system... (true, when I start reading any NFPA code, my eyes start to bleed.. so maybe I've missed something)
