• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Fire Trucks access road

Jaber Alhaji

Registered User
Joined
Dec 23, 2017
Messages
41
Location
Dammam
We are finalizing the Fire Apparatus Access road layout for project. We have the following queries –

Query #1:

Section 503.1.1 of IFC 2018 , which requires an approved fire apparatus access road for every facility such that such roads are within 45 m of all portions of the facility. The code does note that the fire code official is authorized to increase this distance where the building is protected by the Automatic Sprinkler System. However, the code does not mention the extent of such an increase. your insight is highly appreciated

Query #2:

There is an appendix D in the IFC which provides a further requirement for Fire Apparatus Access Road. However, this appendix D is not mandatory and is subject to adopting ordinance. Dose the appendixes be part of the Code?
 
Q 2. Only if adopted or contract says comply with.

Q 1. Up to the person enforcing it… Plus normally case by case, depending on extent of project
 