Good Afternoon,
I think I know the answer to this, but was hoping to bounce it off you all for verification. 2018 IBC is the adopted Code by the way...
I am working on a mixed-use building containing several occupancy classifications including one residential dwelling unit (R3). Section 903.2.8 reads that "An automatic sprinkler system installed in accordance with Section 903.3 shall be provided Throughout all BUILDINGS with a Group R Fire area." Based on this language, it is my understanding that the entire building needs to be needs to be sprinkled. This requirement is further confirmed in the commentary.
Regarding Fire Walls, my understanding is that they serve to create separate "buildings". My question is this: If one were to construct a fire wall to separate the R3 occupancy from the others, thereby creating "separate" "buildings", would that allow me to eliminate the sprinkler from the other occupancies and only include for the residential occupancy?
The commentary for section 706 seems to indicate that a Fire Wall creates "separate buildings", but only in terms of "allowable area, allowable height and type of construction requirements" and that "Using these provisions to control other building features or elements such as means of egress, building systems or building utilities is not intended or implied by the provisions".
Based on the commentary, it would seem that a Fire Wall would NOT eliminate the requirement for a sprinkler system throughout, or on both sides of the Fire Wall.
Do you agree?
Thanks in advance for your help!
-Ryan
I think I know the answer to this, but was hoping to bounce it off you all for verification. 2018 IBC is the adopted Code by the way...
I am working on a mixed-use building containing several occupancy classifications including one residential dwelling unit (R3). Section 903.2.8 reads that "An automatic sprinkler system installed in accordance with Section 903.3 shall be provided Throughout all BUILDINGS with a Group R Fire area." Based on this language, it is my understanding that the entire building needs to be needs to be sprinkled. This requirement is further confirmed in the commentary.
Regarding Fire Walls, my understanding is that they serve to create separate "buildings". My question is this: If one were to construct a fire wall to separate the R3 occupancy from the others, thereby creating "separate" "buildings", would that allow me to eliminate the sprinkler from the other occupancies and only include for the residential occupancy?
The commentary for section 706 seems to indicate that a Fire Wall creates "separate buildings", but only in terms of "allowable area, allowable height and type of construction requirements" and that "Using these provisions to control other building features or elements such as means of egress, building systems or building utilities is not intended or implied by the provisions".
Based on the commentary, it would seem that a Fire Wall would NOT eliminate the requirement for a sprinkler system throughout, or on both sides of the Fire Wall.
Do you agree?
Thanks in advance for your help!
-Ryan