1. Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by clicking here: Upgrades
    Dismiss Notice

Fire Wall or Fire Rated wall?

Discussion in 'Commercial Building Codes' started by Mech, Jun 14, 2019.

  1. Mech

    Mech Sawhorse

    Joined:
    Oct 30, 2009
    Messages:
    766
    Likes Received:
    20
    2015 IBC

    Existing building with F-1, S-1, S-2, B use groups. Proposed addition with F-1 and S-2 use groups.

    I need to separate a 40 ft tall proposed addition from a 27 ft tall existing building with fire rated construction. The speed humps I encounter are that the structural engineer wants the addition to be about 3 feet from the existing building to minimize roof strengthening requirements due to snow drift loads on the existing lower roof and the owner wishes to retain a courtyard to maintain existing refrigeration equipment.

    Since the proposed 3 hour FIRE RATED wall is not immediately adjacent to all existing building walls,
    1. Can this still be considered a 3 hour rated FIRE WALL to create separate buildings?
    2. Are the existing Type 3B non-rated building walls in violation of Table 602 for not having a minimum 30 ft fire separation distance?
    3. Can the unrated overhead door be placed in the unrated wall?

    Thanks

    [​IMG]
     
  2. RLGA

    RLGA Sawhorse

    Joined:
    Oct 18, 2009
    Messages:
    1,722
    Likes Received:
    544
    First, what is driving the need for a fire wall? Does the combined area of the existing building and addition exceed the allowable area for the most restrictive construction type? Second, can the buildings be considered as separate buildings with an imaginary lot line between them?
     
  3. steveray

    steveray Sawhorse

    Joined:
    Nov 25, 2009
    Messages:
    6,530
    Likes Received:
    886
    Seems like it doesn't NEED to be a firewall, 2 buildings same lot FSD rated only.....
     
  4. Mech

    Mech Sawhorse

    Joined:
    Oct 30, 2009
    Messages:
    766
    Likes Received:
    20
    The existing building plus addition exceeds the maximum allowable area, even with sprinklers and frontage increase. The unlimited area building classification does not work due to the presence of an existing third floor.

    The addition must be connected to the existing building with weathertight construction (walls and roof.) I see that my initial sketch missed a wall on the top side of the overhead door openings (and obscured by the nice photobucket ad); it's in there now.
     