I have a contractor venting a large gas fireplace in a lower level up through a 1 hour concrete floor/ceiling assembly, then out the sidewall. 2012 IBC. The vent is 10" diameter b vent. Would the "vent" listed in 714.4.1.1 apply here, so a shaft would not be required?

714.4.1.1 Through penetrations.

Through penetrations of fire-resistance-rated horizontal assemblies shall comply with Section 714.4.1.1.1 or 714.4.1.1.

Exceptions:

1. Penetrations by steel, ferrous or copper conduits, pipes, tubes or vents or concrete or masonry items through a single fire-resistance-rated floor assembly where the annular space is protected with materials that prevent the passage of flame and hot gases sufficient to ignite cotton waste when subjected to ASTM E 119 or UL 263 time-temperature fire conditions under a minimum positive pressure differential of 0.01 inch (2.49 Pa) of water at the location of the penetration for the time period equivalent to the fire-resistance rating of the construction penetrated. Penetrating items with a maximum 6-inch (152 mm) nominal diameter shall not be limited to the penetration of a single fire-resistance-rated floor assembly, provided the aggregate area of the openings through the assembly does not exceed 144 square inches (92 900 mm2) in any 100 square feet (9.3 m2) of floor area.
 