• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Firewall over 20 feet tal, table 601

milam@tomanbrothers.

Registered User
Joined
Feb 21, 2024
Messages
1
Location
San Antonio
I have A firewall over 20 feet tall, does table 601 apply, which states members over 20 feet tall do not need to be protected. Under ch. 7 ( 704.1 says to meet table 601) 706.5 states roof needs to be protected 4 ft out ? being over 20 feet does that affect the 4 ft ou ?

This is in A gymnasium over 20 feet from the roof deck to the floor.

Does the deck need to be protected ?
 
Only the 4-foot strip on each side of the fire wall is required to be protected. Table 601 provides general requirements for all buildings of a certain construction type whether fire walls exist or not, while Section 706.5 is a specific requirement that applies only to fire wall applications. Thus, per Section 102.1, the specific requirement has precedence over the general requirement.
 