• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Fitness center Group B vs A-3 based on Occupant load

tonyflux

Registered User
Joined
Nov 2, 2020
Messages
9
Location
United States
I'm calculating the occupant load for a fitness center remodel project in FL. The calculations are between 49-52 depending on defining the net areas (exercise space, offices, lobby etc..) vs gross area calculations.
Are there any design disadvantages for Occupant load becoming 50+which will make it Group A-3?
 
Two exits

How many sq ft??

And what occupant load factor are you using?
 
All doors serving the assembly space to have panic hardware, and it may affect the plumbing fixture calculation.
Thanks. It's an open space, so we have 2 entry doors and one exit door. Entry doors are glass (storefront) doors, Can't put panic hardware. Plumbing fixture calculations ask for less than what's required in Group B.
 