Ceiling fan with no luminaire is being moved to vaulted ceiling. Fixture wires need to be lengthened due to new, longer down rod.
Can a fixture wire splice be made in the down rod? If so...
How do you determine sufficient fill size for the connections? (is the rod large enough?)
How would you insure connections don't come apart when pulled into down rod?
I find this in the NEC, but it's specific for luminaires. This fan has no light. What if it did have a light? Would that change the way the NEC addresses it?
410.56 Protection of Conductors and Insulation (C) Luminaire Stems: Splices and taps shall not be located within luminaire arms or stems.
Thanks.