• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

flex duct support

ICE

Oh Well
Joined
Jun 23, 2011
Messages
12,934
Location
California
There is usually a place or two where the strap has folded and is not 1.5" wide. I didn't see that here.
Do you allow cloth strap for duct support?


 
I frequently see the cloth strapping as pictured and do allow its use. Yes there are times where the straping is folded or pinching the duct, at that point I require the issue to be corrected. More times than not if the duct is pinched it's due to a change in angle and I have no concerns about asking for additional supports and do not encounter resistance.
 
& : & : &


For a fix to a pinched \ restricted duct, a
Hanger Duct Saddle could be used.


duct_saddles.jpg



& : & : &
 
ICE,
ADC Flexible Duct Performance & Installation Standards:

Flexible duct shall be supported at manufactures supported recommendations, not to exceed 5-feet,
not to have more than 1/2-in sag per foot and can be nonmetallic type straps.

You may be a bit saggy looking at your photos, but maybe it meets the manufactures support guidelines??
 
The picture that I used to open this thread does not show any folded cloth strap. I couldn't see any of that from the access scuttle. Had I crawled the attic I most likely would have found a few. I think that over time there will be folded strap as in this picture.


Just knowing that it can turn out like this is reason enough to deny it.
 