I'm aware of sizing & turbulence issues with flex duct but do you see issues with using class 1 flex duct within concealed chase in a SFD from basement through two floors into attic, fire-blocking to be placed at each flr level?
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
That's good news. It will help the fire get from the basement to the attic quicker.The duct will be in a chase throughout the floor levels
I should have put this in my first post but I can not edit so;Gregg Harris said:A flexible air connector as listed in IMC 603.6.2 can only have a maximum length of 14 feet 603.6.3 prohibits it from passing through any wall, floor or ceiling and is listed under UL181 but only has to pass 12 of the 15 tests. It does not get tested for flame rate, puncture or impact and thus limits its use.Regular flex duct can be run vertically but must be supported every 6 feet and straps must be a minimum of 1.5 inches wide, and even though a lot of contractors are using flex duct most do not follow the manufactures instructions for the installation,sizing and end up causing systems to fail upon delivering air to the space as needed and causing equipment failure such as compressors and heat exchangers. Most contractors are not aware of the pressure drop due to the higher friction rate of the flex over galvanized duct.
Each manufacturer of flex has there own friction rate duct calculator that must be used in sizing, just because the dimension is the same between brands does not mean they have the the same number of coils per foot.
Flex when run horizontally must be supported at a maximum interval of 5 feet and installed taught with a maximum of 1/2 in sag in between the supports to prevent additional friction loss and turbulence.
d. When installed in a fire-rated floor/roof ceiling assembly, ducts shall conform with the design of the tested fire-resistive assembly.Daddy-0- said:Don't you also need a metal boot or hard duct when passing through floors? I know you do for returns passing through to crawl spaces and for all duct work passing through a garage common wall.
I was thinking more along the lines of romex and 1/8th inch wide wire ties.Gregg Harris said:Francis are you asking if a nylon tie can be used for the mechanical connection to the bathroom exhaust? The answer would be yes.For support of the duct it would require a strap or support of a minimum of 1.5 inches wide.
Francis Vineyard said:I was thinking more along the lines of romex and 1/8th inch wide wire ties.M1601 are duct systems serving heating, cooling and ventilation equipment. I don't believe the code references specific requirements for bathroom ducts other than shall be exhausted directly to termination when it's required.
IMO there is no right or wrong answer.
Francis[/quote
A bathroom exhaust fan is ventilation equipment for the bathroom, so it is covered by M1601. Also, the listing of the flex duct itself requires the wider straps