What have you guys seen to meet the requirements of 2006 IBC 712.4 for floor drains and floor sinks in a fire rated concrete floor?
In retro work (or where missed in a new pour), a fairly large core drill needs to be made, then the drain is inserted into the hole. Even if this were pookied in with red goop, this leaves a lot of exposed metal that is not anywhere close to being equivalent to the minimum 5" of concrete needed for the rating. Even in a new pour, where the drain body is cast into the floor, a large floor drain or a floor sink will create a pretty big area of non-concrete.
I don't think this meets any of the exceptions listed in 712.4.1.1, and therefore must meet either 712.2.1.1.1 or 712.4.1.1.2. I doubt floor drains and sinks are included in the fire resistance rating tests of the assembly, so 712.1.1.1 is out, and I have not been able to find a T rated ASTM E 814 fire stopping system to meet 712.4.1.1.2. All the T ratings are for full pipe penetrations, not drains, and usually require insulation. Plenty of F ratings - no T.
The intent of a T rating is to limit the radiant heat from the fire-side from auto-igniting materials on the non-fire side. Just putting some red pooky around a metal floor drain/sink body does not address the radiant issue.
I will continue to look for a T rating, but it made me wonder why did this just now come up in a project - I have seen the bottom of metal floor drains/sinks in a lot of buildings.
In retro work (or where missed in a new pour), a fairly large core drill needs to be made, then the drain is inserted into the hole. Even if this were pookied in with red goop, this leaves a lot of exposed metal that is not anywhere close to being equivalent to the minimum 5" of concrete needed for the rating. Even in a new pour, where the drain body is cast into the floor, a large floor drain or a floor sink will create a pretty big area of non-concrete.
I don't think this meets any of the exceptions listed in 712.4.1.1, and therefore must meet either 712.2.1.1.1 or 712.4.1.1.2. I doubt floor drains and sinks are included in the fire resistance rating tests of the assembly, so 712.1.1.1 is out, and I have not been able to find a T rated ASTM E 814 fire stopping system to meet 712.4.1.1.2. All the T ratings are for full pipe penetrations, not drains, and usually require insulation. Plenty of F ratings - no T.
The intent of a T rating is to limit the radiant heat from the fire-side from auto-igniting materials on the non-fire side. Just putting some red pooky around a metal floor drain/sink body does not address the radiant issue.
I will continue to look for a T rating, but it made me wonder why did this just now come up in a project - I have seen the bottom of metal floor drains/sinks in a lot of buildings.