Floor joist to 'rat slab' clearance
Rio
Silver Member
The clearance from grade to the bottom of floor joists in enclosed areas, such as crawl spaces under a house, is per the CRC/IRC 18"
R317.1 Location required. Protection of wood and wood
based products from decay shall be provided in the following
locations by the use of naturally durable wood or wood that is
preservative-treated in accordance with AWPA Ul for the species,
product, preservative and end use. Preservatives shall be
listed in Section 4 of AWPA Ul.
1. Wood joists or the bottom of a wood structural floor
when closer than 18 inches (457 mm) or wood girders
when closer than 12 inches (305 mm) to the exposed
ground in crawl spaces or unexcavated area located
within the periphery of the building foundation.
We have a situation where there is a concrete slab where the grade is and from the top of that slab it's about 14" to the bottom of the floor joists. We've had this situation before in doing remodel additions and there's never been an issue but now there is. The inspector wants the slab removed or pressure treated joists used. I'm trying to find a code section that addresses this issue and haven't found anything except for the one above which does in a roundabout way. Does anyone know of a more specific citation?
Any suggestions would be appreciated,
Rio
Rio said:
The clearance from grade to the bottom of floor joists in enclosed areas, such as crawl spaces under a house, is per the CRC/IRC 18"R317.1 Location required. Protection of wood and wood
Rio
to the exposed
Gregg gave you the answer.....here's a little more ammo
R317.1 Location required. Protection of wood and wood based products from decay shall be provided in the following
locations by the use of naturally durable wood or wood that is preservative-treated in accordance with AWPA U1 for the species,
product, preservative and end use. Preservatives shall be listed in Section 4 of AWPA U1.
1. Wood joists or the bottom of a wood structural floor when closer than 18 inches (457 mm) or wood girders
when closer than 12 inches (305 mm) to the exposed ground in crawl spaces or unexcavated area located
2. All wood framing members that rest on concrete or masonry exterior foundation walls and are less than 8
inches (203 mm) from the exposed ground.
3. Sills and sleepers on a concrete or masonry slab that is in direct contact with the ground unless separated from such slab by an impervious moisture barrier.
Jobsaver said:
Is exposed ground still exposed ground when covered by an impervious moisture barrier? What say you code geeks of ole?
Well no....it's ground covered by an impervious moisture barrier. Exposed ground isn't shovel resistant like impervious ground.
Thanks for all the replies. I would say from reading and thinking on it the question is 'Is a slab considered the same as exposed ground?' I read the interesting attachment that Mark posted and according to that, it is considered the same even though it is obviously not. What's funny about that is when I was involved directly in construction, it was in San Diego and this issue came up several times and was signed off on no problem. That is why I was taken aback when it came up this time.
Thinking on the intent of this code section I would guess that the intent is to keep moisture a good distance from the wood. This does bring up the question of why is it okay for a girder to be 12" and a floor joist has to be 18"? From reading the attachment from the city of San Diego it appears that moisture is the concern also as if the slab has a moisture barrier under it then it's okay for the slab to be less than 18" to the bottom of the joists.
I posted this also on Contractor talk and someone suggested a solution might be to lay 6 mil plastic over the top of the slab, lapped 6" and sealed. Any feedback on that idea? I'm also now thinking that a possible solution if moisture is the issue might be to seal the top of the slab with a water sealer or a low permeable paint.
Thanks again for all the comments and any suggestions,
Rio
That is what the code allows. I have approved that several times.
If the wood can be 6 mils away from the concrete, 14" shouldn't be a problem. I would use 10 mil because it stands up better while construction takes place.
As a side note I included the ventilation requirement to show how effective the IMB is held to be.
IBC
2. The total area of ventilation openings is permitted to be
reduced to 1/1,500 of the under-floor area where the
ground surface is covered with a Class I vapor retarder
material and the required openings are placed so as to
provide cross ventilation of the space. The installation
of operable louvers shall not be prohibited.
IRC
R408.1 Ventilation. The under-floor space between the bottom
of the floor joists and the earth under any building (except
space occupied by a basement) shall have ventilation openings
through foundation walls or exterior walls. The minimum net
area of ventilation openings shall not be less than 1 square foot
(0.0929 m2) for each 150 square feet (14 m2) of under-floor
space area, unless the ground surface is covered by a Class 1
vapor retarder material. When a Class 1 vapor retarder material
is used, the minimum net area of ventilation openings shall not
be less than 1 square foot (0.0929 m2) for each 1,500 square
feet (140 m2) of under-floor space area. One such ventilating
opening shall be within 3 feet (914 mm) of each corner of the
building.
http://www.finehomebuilding.com/item/5090/whats-the-difference-vapor-barriers-and-vapor-retarders
Here's the update on the concrete slab being less than 18" to the floor joists. I just got off the phone with the plan checker and he said the concern they had is not with vapor coming up from below the slab but a plumbing leak getting the slab wet and then the concrete letting the slab hold the water. He said they discussed it with the B.O. and the contractor and agreed to jackhammer the slab enough to allow any water that might get on top of the slab to work its way down to the earth and be soaked up by the ground. Thanks again to all for their feedback and a special thanks to Mark and ICE.
That's the most ridiculous thing I've ever heard.
WOW.
From the 2006 IRC Q&A:
Q "If the wood joists were 17 " from the exposed ground in the crawl space within the periphery of the foundation and an approved poly vapor barrier was laid on top of the exposed ground, would those joists still need to be treated...."
A "NO"
Of course the Q&A doesn't cover spills!
By this logic - we should jackhammer holes in all basement floors. Right?
Darn, now I've gotta crawl back under there and fork the plastic
No. All buildings with concrete floors!
Actually jackhammering holes in the slab is only going to increase the possibility that moisture will now come from those silly holes.