• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Florida Building Code - Concrete Testing Reports

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,063
Location
Somewhere Too Hot & Humid

1703.6.2Test and inspection records.​

Copies of necessary test and special inspection records shall be filed with the building official.

1703.6.2.1Concrete testing reports.​

Where this code, a referenced standard, a building official or inspection agency requires testing of concrete on a project, test reports shall be provided to the building official or inspection agency, the registered design professional of record, and the material supplier concurrent when reporting results to the client.
 
Not seeing a question, so I speculate you are sharing to see where the discussion leads... so I'll lead off with a comparison to the base IBC.

In the unamended 2021 IBC, this is covered via Sec. 1704.2.4, in conjunction with Sec. 1705.3 - Concrete Construction. Not quite as specific regarding concrete testing, but between the this and Table 1705.3, you get to the same requirement.

2021 IBC 1704.2.4 Report Requirement

Approved agencies shall keep records of special inspections and tests. The approved agency shall submit reports of special inspections and tests to the building official and to the registered design professional in responsible charge. Reports shall indicate that work inspected or tested was or was not completed in conformance to approved construction documents. Discrepancies shall be brought to the immediate attention of the contractor for correction. If they are not corrected, the discrepancies shall be brought to the attention of the building official and to the registered design professional in responsible charge prior to the completion of that phase of the work. A final report documenting required special inspections and tests, and correction of any discrepancies noted in the inspections or tests, shall be submitted at a point in time agreed upon prior to the start of work by the owner or the owner's authorized agent to the building official.
 