Hello. First time posting and appreciate any help. I am located in the Northeast (zone 4a) and am working on a project with a rainscreen wall assembly. Per ASHRAE 90.1, we have foil faced polyiso as our continuous insulation that creates the drainage plane in our drained and vented cavity of our rain screen behind our exterior metal panel. Our metal panel is held off by thermally broken z-girts. We were calling for the seams of the polyiso to be sealed so that water can’t be absorbed into the cut ends of the polyiso. I know this also forms a class 1 vapor retarder. Behind the polyiso, the contractor has already installed a separate liquid applied WRB to the face of exterior gypsum board sheathing. The gyp sheathing is on metal studs with cavities filled with Batt insulation. I have 2 questions:
1.) ASHRAE calls for continuous insulation, which by nature of the polyiso product forms a class 1 vapor retarder on the exterior of the wall assembly. Does this present an issue in a zone 4A location? We have called for latex paint as the interior finish which is also a class III vapor retarder to allow for the wall to “dry” to the interior.
2.) is there any issue having the sealed edge continuous polyiso insulation with the separate WRB behind it? The perm rating of the WRB is 19. The contractor also had said he was not intending to seal the polyiso seams since the WRB was behind it and would handle any water. I believe this is incorrect and he would still need to seal the seams.
Again, any insights would help. Thanks!
1.) ASHRAE calls for continuous insulation, which by nature of the polyiso product forms a class 1 vapor retarder on the exterior of the wall assembly. Does this present an issue in a zone 4A location? We have called for latex paint as the interior finish which is also a class III vapor retarder to allow for the wall to “dry” to the interior.
2.) is there any issue having the sealed edge continuous polyiso insulation with the separate WRB behind it? The perm rating of the WRB is 19. The contractor also had said he was not intending to seal the polyiso seams since the WRB was behind it and would handle any water. I believe this is incorrect and he would still need to seal the seams.
Again, any insights would help. Thanks!