i am confused. what specifically does the roof top unit serve and how many floorsEach hotel room will have its own a/c unit.
606.2.1 Return air systems.
Smoke detectors shall be installed in return air systems with a design capacity greater than 2,000 cfm (0.9 m3/s), in the return air duct or plenum upstream of any filters, exhaust air connections, outdoor air connections, or decontamination equipment and appliances.
i am confused. what specifically does the roof top unit serve and how many floors
No return, no smoke detector. Just have to wonder how you balance such a system.
pick one that works with what you have
2012 IMC
606.2 Where required.
Smoke detectors shall be installed where indicated in Sections 606.2.1 through 606.2.3.
Exception: Smoke detectors shall not be required where air distribution systems are incapable of spreading smoke beyond the enclosing walls, floors and ceilings of the room or space in which the smoke is generated.
606.2.1 Return air systems.
Smoke detectors shall be installed in return air systems with a design capacity greater than 2,000 cfm (0.9 m3/s), in the return air duct or plenum upstream of any filters, exhaust air connections, outdoor air connections, or decontamination equipment and appliances.
Exception: Smoke detectors are not required in the return air system where all portions of the building served by the air distribution system are protected by area smoke detectors connected to a fire alarm system in accordance with the International Fire Code. The area smoke detection system shall comply with Section 606.4.
606.2.2 Common supply and return air systems.
Where multiple air-handling systems share common supply or return air ducts or plenums with a combined design capacity greater than 2,000 cfm (0.9 m3/s), the return air system shall be provided with smoke detectors in accordance with Section 606.2.1.
Exception: Individual smoke detectors shall not be required for each fan-powered terminal unit, provided that such units do not have an individual design capacity greater than 2,000 cfm (0.9 m3/s) and will be shut down by activation of one of the following:
1. Smoke detectors required by Sections 606.2.1 and 606.2.3.
2. An approved area smoke detector system located in the return air plenum serving such units.
3. An area smoke detector system as prescribed in the exception to Section 606.2.1.
In all cases, the smoke detectors shall comply with Sections 606.4 and 606.4.1.
606.2.3 Return air risers.
Where return air risers serve two or more stories and serve any portion of a return air system having a design capacity greater than 15,000 cfm (7.1 m3/s), smoke detectors shall be installed at each story. Such smoke detectors shall be located upstream of the connection between the return air riser and any air ducts or plenums.
[F] 606.3 Installation.
Smoke detectors required by this section shall be installed in accordance with NFPA 72. The required smoke detectors shall be installed to monitor the entire airflow conveyed by the system including return air and exhaust or relief air. Access shall be provided to smoke detectors for inspection and maintenance.
NFPA 72 2013 Section 17.1.5.3.1 requires a detector on the supply side as required by NFPA 90A
Could also tell you if the bldg next door is on fire.for a supply only ventilation system you could put a smoke detector on the supply duct and it could tell you if the motor in the unit is burning up but it is not required.
Problematic with any type of smoke/duct detector in hot humid locations - be more of a nuisance than a help - besides, it would be jumped out in a few months especially if along a coastal salt air region. Best advice, do a global shutdown when Fire Alarm is activated and move on......
Had more than one elevator shaft with troubles or supervisory issues in our coastal town.
Technology is great for laboratory conditions, field conditions will give you headaches and heartaches to the point you eliminate the technology and have wasted the owner's monies with excessive maintenance cost and creating a divine public hatred for Fire Marshals everywhere.