• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Fuel Gas Exaust Vent

Rider Rick

Silver Member
Joined
Oct 19, 2009
Messages
468
In the 2006 IRC, IMC and IFC is there a section for fuel gas exhaust vent clearances to combustibles?

In a garage is a gas water heater with a single wall exhaust vent running through an attic and out the roof.

Thank you,

Rick
 
Re: Fuel Gas Exaust Vent

See IFGC 503.7 also. Single wall vent pipe can only go from the appliance directly to the outdoors with no other spaces in between. Also 503.7.6 specifically prohibits single wall pipe in attics. b vent or chimney required
 
Re: Fuel Gas Exaust Vent

If this is residential then look at section G2727.7 for single wall metal pipe requirements for gas appliances. IFGC and IMC are applicable only to commercial projects. It cannot originate in or pass through an attic or concealed space. Section G2427.7.7 deals with clearances to combustibles.
 
Top