Ok, what is your take on the following section of the fire resistance design manual?
I have a plan wherein they want to run water supply lines through the fire wall (req'd due to building size) and utilize fire caulking. Typical supply lines are PEX, but will have a section (24-in) of copper pipe penetrating the fire wall with the annular space sealed with fire caulking.
My challenge to the design team, is that although through penetrations are permitted by IBC 706.9 / 714, the GA Manual, which is the listing they are proposing, does not permit "Openings and through penetrations, including protected openings and penetrations". (see highlighted text in image) The listing is more specific than the IBC, so it should prevail in my opinion.
I am reaching out to the GA as well as you folks here to see what the thoughts are.

I have a plan wherein they want to run water supply lines through the fire wall (req'd due to building size) and utilize fire caulking. Typical supply lines are PEX, but will have a section (24-in) of copper pipe penetrating the fire wall with the annular space sealed with fire caulking.
My challenge to the design team, is that although through penetrations are permitted by IBC 706.9 / 714, the GA Manual, which is the listing they are proposing, does not permit "Openings and through penetrations, including protected openings and penetrations". (see highlighted text in image) The listing is more specific than the IBC, so it should prevail in my opinion.
706.9 Penetrations
Penetrations of fire walls shall comply with Section 714.
714.3.1.2 Through-Penetration Firestop System
Through penetrations shall be protected by an approved penetration firestop system installed as tested in accordance with ASTM E814 or UL 1479, with a minimum positive pressure differential of 0.01 inch (2.49 Pa) of water and shall have an F rating of not less than the required fire-resistance rating of the wall penetrated.
Penetrations of fire walls shall comply with Section 714.
714.3.1.2 Through-Penetration Firestop System
Through penetrations shall be protected by an approved penetration firestop system installed as tested in accordance with ASTM E814 or UL 1479, with a minimum positive pressure differential of 0.01 inch (2.49 Pa) of water and shall have an F rating of not less than the required fire-resistance rating of the wall penetrated.
I am reaching out to the GA as well as you folks here to see what the thoughts are.