GA ASW 0810

Sifu

SAWHORSE
Joined
Sep 3, 2011
Messages
3,393
A proposal has come in substituting the gypsum panels in ASW 0810. The assembly calls for 2 layers of 1" shaft liner. The proposed substitution is to replace the 2 1" layers with 4 1/2" layers of shaft liner. I can find no basis to approve this in the GA manual explanatory notes or in the UL guide info. I do find notes that the dimensions listed are minimums. Anyone encountered this before? As far as I know there is no such thing as 1/2" shaft liner.
 
You are correct, there is no such thing as 1/2-inch shaftliner--that is called 1/2-inch gypsum board.

That compromise would not be within the acceptable conditions outlined by GA. However, they are free to have the assembly tested to see if it will work.
 
You are correct, there is no such thing as 1/2-inch shaftliner--that is called 1/2-inch gypsum board.

That compromise would not be within the acceptable conditions outlined by GA. However, they are free to have the assembly tested to see if it will work.
I wrote the OP back when I assumed it would take GA a long time to respond to my inquiry. Kudos to them, they confirmed my position within minutes. Customer service is worth it's weight in gold! DP will find another assembly.
 