Only an engineer can determine the neutral axis of the beam, therefore, without and engineer (which is the case here) the splice not over a column is a violation of the IRC.Looks to be 3 plies, and both face plies are discontinuous over one opening?
Is the middle ply continuous over the opening, and if so does one ply have sufficient capacity for the gravity load?
Is the spliced portion of the beam part of the lateral force resisting system, and if so, is one ply sufficient for that?
Cheers, Wayne
If the spliced ply could have just been deleted, and still comply with the IRC header span (and braced wall segment) requirements, the presence of the spliced ply is not a violation. Hence my various questions.Only an engineer can determine the neutral axis of the beam, therefore, without and engineer (which is the case here) the splice not over a column is a violation of the IRC.
The connection of the butt-end splices can be compliant if designed properly. They can add plywood or metal plates with through bolts, but it has to be designed.If the spliced ply could have just been deleted, and still comply with the IRC header span (and braced wall segment) requirements, the presence of the spliced ply is not a violation. Hence my various questions.
Cheers, Wayne
It only has to be designed if that ply is structurally required. If it's a bonus ply put there for some other reason, like drywall backing, no design required.The connection of the butt-end splices can be compliant if designed properly. They can add plywood or metal plates with through bolts, but it has to be designed.
Looks to be 3 plies, and both face plies are discontinuous over one opening?
Is the middle ply continuous over the opening, and if so does one ply have sufficient capacity for the gravity load?
Is the spliced portion of the beam part of the lateral force resisting system, and if so, is one ply sufficient for that?
Cheers, Wayne
What do the approved plans show over the garage doors?
I don't know, but I do know, it would never show it like that. This was shared to me by the BCO.What do the approved plans show over the garage doors?
Agreed with respect to IRC Table R602.7(1) "Girder Spans and Header Spans for Exterior Bearing Walls," which includes entries for single ply members and would be applicable to the OP.Maybe someday, there will be span tables for headers, built-up beams, and girders in the IRC that will have reductions for splices. Until then, the tables are not based on any splices.
Wayne, the span ratios you mention are interesting, and I agree that they seem to reflect deflection-limited behavior. However, engineers put the IRC tables together, and their reasoning or intent isn’t fully explained in the code. They’re meant as a prescriptive method, so we follow them as written without knowing all the assumptions behind them.Agreed with respect to IRC Table R602.7(1) "Girder Spans and Header Spans for Exterior Bearing Walls," which includes entries for single ply members and would be applicable to the OP.
But as an aside, IRC Table R602.7(2) "Girder Spans and Header Spans for Interior Bearing Walls" includes entries only for two, three, and four ply members. And if for a given ply size and loading condition, you calculate the ratio of spans, you will find that the 4 ply span / 2 ply span is very close to the cube root of 3, while the 3 ply span / 2 ply span is very close to the cube root of 2. [I didn't exhaustively check this for all loading conditions, just a representative few.]
That would be consistent with the spans being deflection limited (so the cubic behavior) and based on one less continuous ply than the number listed. I.e. on one ply being disregarded, for whatever reason.
A quick scan of the IRC didn't turn up any text discussing this question--did I miss anything? If not, is one ply disregarded because it's allowed to be spliced over any given span? Or is one ply disregarded as an added factor of safety to account for other material/installation variations, and all girder ply splices must be over supports?
Cheers, Wayne
Just wanted to check that there isn't some text describing girder installation in part of the IRC I overlooked, which text might specify that a splice in one ply between supports is already built into the calculated spans and is allowed. I agree that absent such text, all splices of required plies of a girder must be over supports, even though the prescriptive spans in the Table seem to be disregarding one girder ply already.Wayne, the span ratios you mention are interesting, and I agree that they seem to reflect deflection-limited behavior. However, engineers put the IRC tables together, and their reasoning or intent isn’t fully explained in the code.
But I hope we agree that if the girder span table says that (2) 2x12s is sufficient for a given loading condition, and I install (3) 2x12s but let them run wild, so that over each span there are 0 or 1 unsupported splices (always on an outer ply for simplicity, so that the two continuous plies are adjacent), that complies with the IRC. Yes?
You gave a good answer as to how the scenario I described might not comply with the approved construction drawings. But my statement was just "that complies with the IRC," not "complies with the construction drawings" or "should pass inspection."Because I'm "that guy," I'm going to say that I don't agree.
Thread Drift AlertSo the garage door header is sized on the drawings to allow for the possible future second floor as well as the roof. The contractor doesn't know this, so he doesn't build the header as designed, and as shown on the approved construction documents.
To follow up on this aside, I checked the 2018 Wood Frame Construction Manual, and Table 3.24A2 has identical values as IRC Table R602.7(2), while also covering single ply 2x6 to 2x12 header/girders. So that falsifies the idea the table is based on only n-1 continuous plies in a built-up header, as 1 ply would then have 0 capacity.But as an aside, IRC Table R602.7(2) "Girder Spans and Header Spans for Interior Bearing Walls" includes entries only for two, three, and four ply members. And if for a given ply size and loading condition, you calculate the ratio of spans, you will find that the 4 ply span / 2 ply span is very close to the cube root of 3, while the 3 ply span / 2 ply span is very close to the cube root of 2. [I didn't exhaustively check this for all loading conditions, just a representative few.]
This might be a great subject to reintroduce and expand upon in the engineering section of the forum. Thoughts?To follow up on this aside, I checked the 2018 Wood Frame Construction Manual, and Table 3.24A2 has identical values as IRC Table R602.7(2), while also covering single ply 2x6 to 2x12 header/girders. So that falsifies the idea the table is based on only n-1 continuous plies in a built-up header, as 1 ply would then have 0 capacity.
I think the observations about cube root of 2 and cube root of 3 are just coincidences. I imported all the spans into a spread sheet, and looked at the ratio of allowable spans for n plies vs just 1 ply, for different member sizes and building widths. Pretty consistently the ratios are 1 for n=1 (obviously), 1.48 for n=2 (range 1.4 to 1.5), 1.86 for n=3 (range 1.84 to 1.87), and 2.15 for n=4 (range 2.13 to 2.16).
If we square those numbers (as would be appropriate for the strength controlled case, rather than the deflection controlled case), we get squared ratios of 2.2, 3.45, and 4.62 for n=2,3, and 4, respectively. The last two cases correspond well with n * 1.15, which is the repetitive member factor the NDS allows for 3 or more members. I'm still unclear on why the square ratio for n=2 is 2.2 ratio rather than just 2.0.
Cheers, Wayne
As much as I want to agree....The prescriptive PFs require a min 3" wide header....Engineering...It only has to be designed if that ply is structurally required. If it's a bonus ply put there for some other reason, like drywall backing, no design required.
Cheers, Wayne