Dealing with a middle school final. The building is split level because of the slope of the area. Ground level is the main entrance. As you look to the left the fall of the land allows the building to be at a lower level.
There are stairs leading down to the lower level. This is the area that the architect is saying that since these stairs are not part of the exit access that the gaurds are not required to meet the requirements for gaurds because the specifications for gaurds are in the "Means of Egress" section.
The gaurds are 42" high and have a vertical bar at 32". That leaves about a 9" space between the top of the gaurd to the vertical bar. My interpreatation is that since section 1013 specifies "all" gaurds (with exceptions)...that means ALL gaurds, even if the gaurds are not part of the exit access.
What are yall's thoughts?
There are stairs leading down to the lower level. This is the area that the architect is saying that since these stairs are not part of the exit access that the gaurds are not required to meet the requirements for gaurds because the specifications for gaurds are in the "Means of Egress" section.
The gaurds are 42" high and have a vertical bar at 32". That leaves about a 9" space between the top of the gaurd to the vertical bar. My interpreatation is that since section 1013 specifies "all" gaurds (with exceptions)...that means ALL gaurds, even if the gaurds are not part of the exit access.
What are yall's thoughts?